What do yall think of this:
One bank of AGM'S and one bank of flooded batteries in one cabinet tied with a switch so you could use either bank.I do understand the hydrogen build up from flooded batteries,but if cabinet was ventilated before operating switch what do yall think?
Title: Re: Two Banks in One Cabinet
Post by: vtmaps on February 23, 2014, 04:01:34 AM
What's the point?  How does two battery banks fit into your usage pattern?

It seems that sooner or later you are bound to apply flooded voltages to the AGM bank (bad).

I presume that your switch would be break-before-make?

--vtMaps
Title: Re: Two Banks in One Cabinet
Post by: tcva357 on February 23, 2014, 09:53:33 AM
Yes it would be a tie switch,i have a set of golf cart batteries on a charger that I thought I could rotate between the agm's