Battery talk (A place to discuss any and all battery technologies where the discussion may not fit into other topic areas) => Lead Acid (Sealed and flooded) => Topic started by: Syonyk on February 07, 2018, 04:00:42 PM

Title: Where do you set your WbJr end amps for FLA?
Post by: Syonyk on February 07, 2018, 04:00:42 PM
I know the datasheets typically say "1-3% of C/20 rate" for charge termination, but that's an awfully wide range.

For a 225Ah bank, that's 2.25A-6.75A, which is quite a wide range for termination.  Especially since, given enough charging, it can get down to the 1% area.

I've had it set around 1% for the winter, which it can get to (sometimes not after a long week of PSOC cycling), but I'm thinking that pushing it up to 1.5% or 2% in the summer, when the pack charges fully every day, would be sane.

Thoughts?  My goal is longevity on the bank, more than cramming every last amp-hour in, but they're flooded, so they take the overcharge decently.
Title: Re: Where do you set your WbJr end amps for FLA?
Post by: Westbranch on February 07, 2018, 07:19:36 PM
Tell us more about the whole system and how it is configured... brands, capacity etc
Title: Re: Where do you set your WbJr end amps for FLA?
Post by: ClassicCrazy on February 07, 2018, 07:20:06 PM
There are a lot of past detailed discussions about this topic in the forums.

Basically you need to spend some time analyzing your batteries by watching the point where the amps start to level off , in conjunction with the SOC reaching 100 % , and verifying by taking specific gravity readings . Then you will know what the exact ending amps point should be .

Larry
Title: Re: Where do you set your WbJr end amps for FLA?
Post by: Syonyk on February 07, 2018, 09:13:44 PM
Quote from: Westbranch on February 07, 2018, 07:19:36 PM
Tell us more about the whole system and how it is configured... brands, capacity etc

8x Trojan T105-REs in series, for a 48V/225Ah bank.

Midnite Classic with 2280W of panel hung, WbJr for current sensing.

Plus another 570W of east facing panel on a PWM controller - helpful for getting the recovery going early in the morning.

I'm definitely on the overpaneled side of things, and am usually into absorb by around 1100-1130 (sometimes earlier).

Quote from: ClassicCrazy on February 07, 2018, 07:20:06 PM
There are a lot of past detailed discussions about this topic in the forums.

Ok, I'll dig around a bit.  Any good threads you happen to recall?

QuoteBasically you need to spend some time analyzing your batteries by watching the point where the amps start to level off , in conjunction with the SOC reaching 100 % , and verifying by taking specific gravity readings . Then you will know what the exact ending amps point should be .

Would this be the point where, if you leave it at the absorb voltage, the charge current levels off?  I've got charts on that, and 1% seems about right.  I'll check this against SG here in the next few days.
Title: Re: Where do you set your WbJr end amps for FLA?
Post by: ClassicCrazy on February 07, 2018, 10:28:34 PM
you have to go to the first forum page ( where all the topic are listed )   and then search for Ending Amps 
or search set ending amps

If you see comments from Vic  - read those - he knows his stuff !