Title: Changing from L16 Flooded to LiFePO4 Batteries - Wind Question
Post by: The Grand Pooh-Bah on September 17, 2020, 10:10:52 PM
I have a current system that is on L16 12v Flooded Batteries and Im going to convert to 12v LiFePO4 batteries.  I'm fine with the solar portion of the conversion.  My dilemma is with the wind side of this equation.

I have a 12v Missouri Wind & Solar PMA (permanent magnetic alternator)  that can produce 1600w in a hurricane. Not likely here in Idaho. I currently use a Flexguard NC25A-12 control that activates a dump load when the batteries reach a set voltage.  Flexguard says not to use their control on LiFePO4 batteries.

Has anyone here connected a PMA to LiFePO4 batteries and if so how did you do it and which controller?
Title: Re: Changing from L16 Flooded to LiFePO4 Batteries - Wind Question
Post by: mahendra on September 19, 2020, 06:35:18 PM
No but you need to be careful with voltage rise when charging Lifepo4.

I if recall correctly alternators are made to charge car batteries and not deep cycle because of their higher voltage output.
Title: Re: Changing from L16 Flooded to LiFePO4 Batteries - Wind Question
Post by: LightPower on January 22, 2021, 08:52:28 PM
Quote from: The Grand Pooh-Bah on September 17, 2020, 10:10:52 PM
I have a current system that is on L16 12v Flooded Batteries and Im going to convert to 12v LiFePO4 batteries.  I'm fine with the solar portion of the conversion.  My dilemma is with the wind side of this equation.

I have a 12v Missouri Wind & Solar PMA (permanent magnetic alternator)  that can produce 1600w in a hurricane. Not likely here in Idaho. I currently use a Flexguard NC25A-12 control that activates a dump load when the batteries reach a set voltage.  Flexguard says not to use their control on LiFePO4 batteries.

Has anyone here connected a PMA to LiFePO4 batteries and if so how did you do it and which controller?

I have a 3-phase 12v (AC Wild) 1600watt Freedom PMG 9-Blade Turbine (from Missouri) wired into a Pre-Wired VRD (Voltage reduction) Unit w/a Classic 150- via the Aux 1 port. 
The VRD board was gifted to me from Missouri W&S, due to a Mistake they made on my previous setup (a Skymax 440 controller w/ Diversion, incorrectly wired by them).
According to them, the VRD and the Classic is the ONLY Charge Controller they carry that charges Lithium.
Also, a "Dump-Load" will NOT protect a Classic from Over Voltage and can damage it and nullify your Warranty.
-jDub
Title: Re: Changing from L16 Flooded to LiFePO4 Batteries - Wind Question
Post by: Robin on February 07, 2021, 01:31:56 PM
Light Power is correct.