A Forum run by Enthusiasts of MidNite Solar

Battery talk (A place to discuss any and all battery technologies where the discussion may not fit into other topic areas) => Lead Acid (Sealed and flooded) => Topic started by: Dgrblu on October 21, 2020, 02:11:35 PM

Title: Unattended system for 5 months
Post by: Dgrblu on October 21, 2020, 02:11:35 PM
New member. I purchase a cabin with a off grid system. 4.4 kw, six strings of three pv panels (825w/strg), Midnite combiner, Classic 150 CC, Magnum PAE sine inverter,  Magnum exspandable distribution panel, eight Crown CR435 six volt flooded wired in series 48v. 

My question is this, I snowbird in the winter and will be away from the cabin for 5 months. Do I just shut everything down and let the batteries sit for this amount of time. I have been told that the bank can sit idle for several months without them self discharging to zero in that time frame. I'm not liking this option for fear of a big freeze.

I was thinking of leaving the system intact except that I would turn the inverter output ac circuit breaker off and let the panels and classic do it's thing charging the batteries. Should I do this method,  should I do the following parameter changes;
EQ setting to 365 days(Not letting them EQ while away)
Bulk setting to 51 volts
Absorb setting to 51 volts
Float setting to 50 volts
Wanting to use the system to maintain the batteries only without boiling the water off during the 5 months away.

Any suggestions on how to 'winterize' my system without putting a big hurt on things.

TIA
Retired HVAC Tech.
Title: Re: Unattended system for 5 months
Post by: boB on October 21, 2020, 04:50:47 PM
Welcome !

The others here will hopefully chime in here but I would vote for leaving the system on except for loads if you don't need any on.

If you can leave the inverter off, that's good too.

I guess the question is, will there be snow on the panels possibly for an extended time ?  If so, then that might require a bit of thought.  My reasoning there is that the Classic draws a little bit of power even at night.  Not much, maybe 3 or 4 watts but if there is no sun shining on the panels, then the batteries MIGHT drop down until the sun comes out.

I am guessing that the batteries are 12V ?   The Classic will run down to about 5 volts on the battery but there isn't any (if much) energy in the batteries at that level.

Title: Re: Unattended system for 5 months
Post by: mike90045 on October 21, 2020, 04:54:59 PM
See if you can find a STANDBY float charge setting for your batteries, and use that, or maybe 0.1V higher.   Your charge controllers will consume a bit of power at night and you need to replace that usage.

Fully charged batteries will not freeze below the arctic circle (usually)
Title: Re: Unattended system for 5 months
Post by: boB on October 21, 2020, 05:40:40 PM

One thing I worry about when leaving batteries unattended for long periods is that they can sulfate without an absorb charge once in a while.

For lead acid batteries of course.

Maybe Bulk Skip Days might be in order here, like, maybe once per week ??

Just a suggestion.

Title: Re: Unattended system for 5 months
Post by: ClassicCrazy on October 21, 2020, 09:25:59 PM
You might set up skip days , and set the equalize for every 10 days but set it to an absorb voltage and longer absorb time ( like an  hour or two ) so it does what Bob suggested - gets the electrolyte stirred up good to prevent stratification and sulphating .
I would turn the inverter off if not  using it.

I would just use normal float and absorb voltages , and as I said set the equalize to absorb voltage too every 10 days.  The thing is that with no loads the batteries are going to go quickly  to float every day - so that is why you also use skip days so that it will skip some days of trying to fully charge , but then you know every 10 days it will go to absorb for an hour or two and get the batteries topped up well and electrolyte mixed .

Larry
Title: Re: Unattended system for 5 months
Post by: Resthome on October 23, 2020, 12:41:00 AM
Quote from: ClassicCrazy on October 21, 2020, 09:25:59 PM
You might set up skip days , and set the equalize for every 10 days but set it to an absorb voltage and longer absorb time ( like an  hour or two ) so it does what Bob suggested - gets the electrolyte stirred up good to prevent stratification and sulphating .
I would turn the inverter off if not  using it.

I would just use normal float and absorb voltages , and as I said set the equalize to absorb voltage too every 10 days.  The thing is that with no loads the batteries are going to go quickly  to float every day - so that is why you also use skip days so that it will skip some days of trying to fully charge , but then you know every 10 days it will go to absorb for an hour or two and get the batteries topped up well and electrolyte mixed .

Larry

Larry, I am curious why you would set the Classic up to Equalize at all. Especially at the Absorb voltage. If you set Skip Days to 9 days it will float for 9 days an on the 10th day it will do an charge to Absorb set point and terminate after the Absorb time ends if End Amps is turned off. Then it goes back to Float for 9 more days. Am I missing something?
Title: Re: Unattended system for 5 months
Post by: boB on October 23, 2020, 01:19:33 AM
Quote from: Resthome on October 23, 2020, 12:41:00 AM
Quote from: ClassicCrazy on October 21, 2020, 09:25:59 PM
You might set up skip days , and set the equalize for every 10 days but set it to an absorb voltage and longer absorb time ( like an  hour or two ) so it does what Bob suggested - gets the electrolyte stirred up good to prevent stratification and sulphating .
I would turn the inverter off if not  using it.

I would just use normal float and absorb voltages , and as I said set the equalize to absorb voltage too every 10 days.  The thing is that with no loads the batteries are going to go quickly  to float every day - so that is why you also use skip days so that it will skip some days of trying to fully charge , but then you know every 10 days it will go to absorb for an hour or two and get the batteries topped up well and electrolyte mixed .

Larry

Larry, I am curious why you would set the Classic up to Equalize at all. Especially at the Absorb voltage. If you set Skip Days to 9 days it will float for 9 days an on the 10th day it will do an charge to Absorb set point and terminate after the Absorb time ends if End Amps is turned off. Then it goes back to Float for 9 more days. Am I missing something?


And after the seventh day, it went to resting.

Title: Re: Unattended system for 5 months
Post by: ralph day on October 23, 2020, 08:01:13 AM
What a lot of cabin system owners do here in the cold, snowy north is, put a panel (or 2) on a vertical wall dedicated to the batteries.  No charge controller, just wired directly.  Not enough amps to damage things, but enough to keep from complete discharge.  No experience myself, just what I've heard over the years on forums.
Title: Re: Unattended system for 5 months
Post by: ClassicCrazy on October 23, 2020, 11:10:14 AM
Quote from: Resthome on October 23, 2020, 12:41:00 AM
Quote from: ClassicCrazy on October 21, 2020, 09:25:59 PM
You might set up skip days , and set the equalize for every 10 days but set it to an absorb voltage and longer absorb time ( like an  hour or two ) so it does what Bob suggested - gets the electrolyte stirred up good to prevent stratification and sulphating .
I would turn the inverter off if not  using it.

I would just use normal float and absorb voltages , and as I said set the equalize to absorb voltage too every 10 days.  The thing is that with no loads the batteries are going to go quickly  to float every day - so that is why you also use skip days so that it will skip some days of trying to fully charge , but then you know every 10 days it will go to absorb for an hour or two and get the batteries topped up well and electrolyte mixed .

Larry

Larry, I am curious why you would set the Classic up to Equalize at all. Especially at the Absorb voltage. If you set Skip Days to 9 days it will float for 9 days an on the 10th day it will do an charge to Absorb set point and terminate after the Absorb time ends if End Amps is turned off. Then it goes back to Float for 9 more days. Am I missing something?

What you say is a good idea  - I guess I was thinking there still might be some kind of small loads on the system and less skip days .

Larry

Title: Re: Unattended system for 5 months
Post by: mcsarge on October 29, 2020, 08:27:07 AM
In the system I manage in Canada we do the following:

We disable the invertor so that only the charge controllers and my cellular coms gear and Raspberry Pis are powered (very low power requirements). We added what I can the "Winter Panels" which are a set of panels mounted on the wall of the cabin facing south-southeast under the eaves. They are wired to a separate charge controller to the battery pack. We get significant snow and it is not uncommon for the roof panels to be covered for a month at a time so we needed a way to replace the small amount of energy that the com system uses and keep the batteries charged when the main panels are covered. I have not programmed skip days, but I think I will. We had to get a person in Canada to go and top off the water in the batteries since the pandemic no one has been on the island for a year.

Matt
Title: Re: Unattended system for 5 months
Post by: FNG on November 05, 2020, 09:26:00 AM
Quote from: ralph day on October 23, 2020, 08:01:13 AM
What a lot of cabin system owners do here in the cold, snowy north is, put a panel (or 2) on a vertical wall dedicated to the batteries.  No charge controller, just wired directly.  Not enough amps to damage things, but enough to keep from complete discharge.  No experience myself, just what I've heard over the years on forums.

I would caution on this myself, A full battery will not take much current to raise its voltage to a dangerous area. I would use a simple PWM style controller just as a safety net myself