A Forum run by Enthusiasts of MidNite Solar

Home Brew software => Classic / Outback programming and monitoring software => Topic started by: ALBIE on July 19, 2021, 11:38:56 AM

Title: Classic generator start/stop programing?with wizbang jr
Post by: ALBIE on July 19, 2021, 11:38:56 AM
I have Lithium batteries --24 volt system-----  Need to program the whiz-bang jr classic setting's to start generator at soc @35%  and ags off at soc@80% using aux settings
Not sure how to set soc settings

please comment
thanks
albie
Title: Re: Classic generator start/stop programing?with wizbang jr
Post by: Vic on July 19, 2021, 12:27:27 PM
Hi ALBIE,  Welcome to the Forum.

Have you looked at the Classic Manual?   Look under Aux 1 Modes,  it is on page 42 of the manual version, that I have.

Have not used this function for AGS,  here  ...   of course,  you will need a genset that can use a single wire for start/stop,  unless you get some form of AGS controller (IMO).

FWIW,   Vic
Title: Re: Classic generator start/stop programing?with wizbang jr
Post by: SolarMusher on July 19, 2021, 02:26:50 PM
Quote from: ALBIE on July 19, 2021, 11:38:56 AM
I have Lithium batteries --24 volt system-----  Need to program the whiz-bang jr classic setting's to start generator at soc @35%  and ags off at soc@80% using aux settings
Not sure how to set soc settings

please comment
thanks
albie
Hi Albie,
You don't really need AGS to start your genset. If the genset is two wires start, you just have to add a single relay (or DC solid state relay) and control this relay On/Off from the Classic Aux1 (SOC).
Nothing too complicated. As Vic said take look at the Classic manual.