Torque and breakers

Started by Alaska Man, April 21, 2014, 03:12:17 PM

Previous topic - Next topic

Alaska Man

How important is getting the exact torque on the breaker wire lugs? I just screwed then down tight.
(2) 2 panel 230W (920W Array), Classic 150 with Xentrex Freedom Series Charger/Inverter. 12V 880AH/6V AGM Bank wired in series and parallel. Adding another 1,000W of Panels soon, I hope.

Vic

Alaska ,

Many of us lack the correct Torque Drivers.

Suggest,  that without the correct driver,  that you torque all of these connections TIGHT,  and then let them rest over-night or for a couple of days,  and torque them tight, again.

Do NOT use finely stranded cable on any breaker lugs.  19,  or 7 strand cable is fine.

Opinion,  YMMV.   Good Luck,    Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Alaska Man

Thanks.

The local solar guy gave me these end caps to go over the stranded wire ends, but they were to big to fit into the lugs. So I nixed those too. The wire barely fits, 12 volt system.
(2) 2 panel 230W (920W Array), Classic 150 with Xentrex Freedom Series Charger/Inverter. 12V 880AH/6V AGM Bank wired in series and parallel. Adding another 1,000W of Panels soon, I hope.