Started by mike90045, April 24, 2014, 02:52:22 AM

Previous topic - Next topic

mike90045

XW6048 epanel
Been getting high battery voltage alarms from the charge controller, and I went over all the battery interconnects and the terminals in the charge controller with an IR thermometer.

Then, when getting into the ePanel, to prep for the Midnight Controller for the new array, I saw the cause. And all the screws seem tight. Putting in new #4 wire (55A) and buss bar, and that should fix it up. Yow!

So, it would seem that #4 coarse wire would be ok in the buss bar.  Is this a correct assumption ?  Screws were in tight. Till the new bar is here, I'm not messing much with it, as this is a live system.   Any suggestions about conductive copper filled greases for the wires ? 

more photos here  https://www.facebook.com/photo.php?fbid=000000000000000&l=8bc17afb6c
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Vic

Hi Mike,

WOW,  that is UGLY.

You are a technical person,  but,  as you know,  these connections must be very tight,  allowed to rest and then re-torqued.

Have never had this problem,  but charging batteries can create a lot of stress on components,  because it is often a long slog.

Have never used any conductive goop on these connections,   BUT,  would think that NoalOx or very similar compound should not hurt -- any anti-oxidation material intended for electrical connections should be OK.

So these cables had clean and bright copper at the connection to the busses when first installed?

This situation simply has to be the result of contact resistance at the buss connection -- normally torqueing to spec,  and repeating a day or so later should be fine,  unless the cables are far under-rated,  which from your post,  they should not have been.

The additional pics unavailable -- am not a Face-Space member.
Dunno.   Good Luck!     Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Resthome

I'm curious as to what the yellow label in this e-panel is saying. It seems to indicate, although most of it is blocked by the wring, that fine stranding wire be used for something. Anyone know what the complete label said.

And yeah the FB links don't work.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Westbranch

I think I have the same sticker in mine , poor pic attached but readable.

Mike, Just saw that the upper wire is getting black corrosion and charred insulation  too...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Resthome

So according to the label the Battery cable are suppose to be fine strand cables such as the Cobra cables. Those cables on the Battery Plus bus bar are not fine strand cables.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Westbranch

John, you're comment made me look...  wow, look at the strand #'s on these battery cable s

http://www.cobrawire.com/products/battery.php
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

RossW

Quote from: Resthome on April 24, 2014, 11:53:40 PM
So according to the label the Battery cable are suppose to be fine strand cables such as the Cobra cables. Those cables on the Battery Plus bus bar are not fine strand cables.

10 years ago when I made my battery cables (only 35 sq mm about 1AWG), I used a superflex cable, like this:


I had ALMOST gone to the red stuff in this picture, but the cost was prohibitive...
3600W on 6 tracking arrays.
7200W on 2 fixed array.
Midnite Classic 150
Outback Flexmax FM80
16 x LiFePO4 600AH cells
16 x LiFePO4 300AH cells
Selectronics SP-PRO 481 5kW inverter
Fronius 6kW AC coupled inverter
Home-brew 4-cyl propane powered 14kVa genset
2kW wind turbine

Halfcrazy

Quote from: Resthome on April 24, 2014, 11:53:40 PM
So according to the label the Battery cable are suppose to be fine strand cables such as the Cobra cables. Those cables on the Battery Plus bus bar are not fine strand cables.

That label is referring to the big cables that go to and from the breaker to the inverter. Not to that bus bar. We do not want people trying to run 2/0 or 4/0 THHN to the breaker as it would be brutal for them and tough on the breaker.
Changing the way wind turbines operate one smoke filled box at a time

Halfcrazy

#8
I should also point out this is a point of confusion as the little terminal bus bar is labeled "Battery Positive" and it is battery positive but for things like charge controllers or loads not the actual battery. I wonder if a label change may be beneficial. Maybe something like "Battery + for Accessories"

In this particular case this was not the issue but I have seen 3 or 4 people wire there battery to that little bus bar with #4 or #6 thhn and wonder why things melt when the XW draws 6KW.

As seen in the attached picture the Red arrow depicts "Battery positive" and the Green Arrow depicts "Accessory Positive"

As you can see you would not want to try to hook 4/0 THHN to that breaker but in the other side #4 THHN is perfectly manageable to the Accessory bus bar
Changing the way wind turbines operate one smoke filled box at a time

ChrisOlson

When terminating stranded wire in a screw type bus bar you should insert the wire into the smallest hole it will fit in and use a ferrule or tin the wire to prevent damage to the strands.  The process of tightening the screw "grinds" on the wire strands and reduces their cross-section.  If you damage the strands, the termination will not handle the full ampacity of the wire.

It is also difficult to keep the connection tight after it thermal cycles a few times when the strands are damaged and squeezed out to the side of the screw as shown in the photo.  Tinning the wire prevents that.  The screw will "bite" into the tinning and make a good contact surface area to the bus bar, but the tinning will prevent damage to your wire strands.

I'm not sure if tinning meets code for commercial installations (I don't think it does) where stranded wire is terminated in a screw type lug.  But ferrules or Anderson contact lugs do meet code.  For me, tinning the wire has always worked fine and insures a maximum contact wire termination that will stay tight with thermal cycling.  I've had inspectors look at some of my installations and they never said anything about the tinning on the wire.  So I think tinning the stranded wire is "good enough" for the poor man doing his own installation.  I think an inspector would only question it if it happened to burn off and then he'd look at it and go, "Oh yeah - there's your problem - you tinned it instead of using a ferrule."

Resthome

Quote from: Halfcrazy on April 25, 2014, 07:06:55 AM

That label is referring to the big cables that go to and from the breaker to the inverter. Not to that bus bar. We do not want people trying to run 2/0 or 4/0 THHN to the breaker as it would be brutal for them and tough on the breaker.

That makes more sense. Thanks for the clarification, Ryan. It wasn't clear what terminals the label was referring to.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Resthome

Quote from: ChrisOlson on April 25, 2014, 10:46:38 AM
When terminating stranded wire in a screw type bus bar you should insert the wire into the smallest hole it will fit in and use a ferrule or tin the wire to prevent damage to the strands.  The process of tightening the screw "grinds" on the wire strands and reduces their cross-section.  If you damage the strands, the termination will not handle the full ampacity of the wire.

It is also difficult to keep the connection tight after it thermal cycles a few times when the strands are damaged and squeezed out to the side of the screw as shown in the photo.  Tinning the wire prevents that.  The screw will "bite" into the tinning and make a good contact surface area to the bus bar, but the tinning will prevent damage to your wire strands.

I'm not sure if tinning meets code for commercial installations (I don't think it does) where stranded wire is terminated in a screw type lug.  But ferrules or Anderson contact lugs do meet code.  For me, tinning the wire has always worked fine and insures a maximum contact wire termination that will stay tight with thermal cycling.  I've had inspectors look at some of my installations and they never said anything about the tinning on the wire.  So I think tinning the stranded wire is "good enough" for the poor man doing his own installation.  I think an inspector would only question it if it happened to burn off and then he'd look at it and go, "Oh yeah - there's your problem - you tinned it instead of using a ferrule."

+1.

Excellent advise Chris. I tin mine also. Adding the ferrules is great but doesn't always work unless you have a larger hole available in the buss bar.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Westbranch

Any recommendations of ferrules? As my pic shows there is not much room in a standard width E-panel...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Resthome

Quote from: Westbranch on April 25, 2014, 03:26:01 PM
Any recommendations of ferrules? As my pic shows there is not much room in a standard width E-panel...

I'm not using and e-panel here but from the pictures you're correct not a lot of room. You also have to use the correct crimpers with the ferrules.

http://www.ferrulesdirect.com/electrical/WIRE_FERRULES.htm
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

zoneblue

I agree that screw type terminals have issues, and i try to avoid them altogether for anything carrying any current. Crimp, lug and post is a better solution.
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar