1849 wdt resets

Started by zoneblue, June 10, 2014, 01:36:05 AM

Previous topic - Next topic

zoneblue

thanks dgd. im trying to rule out what extra load my logging system might be putting on the classic. I cant really get clear in my mind when these resets started but it was definately post 1760. However i also increased the blackbox sample rate around that time.. i think?
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

Zap

I have seen were kwh’s go back to 0  or start over for no rhyme or reason,  mostly cloudy days going from low to high output , I've also  had a few  lockups, by that I mean the network connection quits responding, a power down power up of the C150  fixes it.
6X Kyocera KD245GX-LFB, 2xClassic 150’s, 2x e-panel, 1x nottagutter 2x Outback-FX2524T, 800ah @ 24 volt battery bank, BBB running the BlackBox

boB

ZoneBlue, (and others), does the Classic reset maybe when it is HOT ?

When was your Classic made or its serial number ?

boB
K7IQ 🌛  He/She/Me

Zap

I have not notice it getting hot.
CL02001

This ones not in service yet but do keep the firmware up to date.
CL02392
6X Kyocera KD245GX-LFB, 2xClassic 150’s, 2x e-panel, 1x nottagutter 2x Outback-FX2524T, 800ah @ 24 volt battery bank, BBB running the BlackBox

zoneblue

4037.  System here doesnt run hot, 15C ambient, 40A throughput. Fan comes on very little. When 1760 came out the resets were mostly early morning or evening. These days i would say the opposite: mid bulk or so.
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

zoneblue

#20
Ok, so i looked at it closer, every reset is during bulk charge stage. Time varys, temp varys.
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar