« on: August 11, 2014, 06:08:10 PM »
To find the "LAST Reason For Resting"

From the main status screen hold the left arrow and tap Enter. The top middle number is the "Last" RFR

Remember this is over written the next time it goes to resting

This table was stolen from a post by boB - hope to make it easier to find:

                      Reason  For Resting:

   ...  "

    ReasonForResting = 1    Wake state, (Vpv < PreVoc AntiClickSenstvty  (MB Addr. 4236)
    ReasonForResting = 2    Insane Ibatt on WakeUp state (offset changed from off state)
    ReasonForResting = 3    Negative current on WakeUp state
    ReasonForResting = 4    dispavgVpv < (dispavgVbatt - 10) Now -25 (RestartTimerms = 1500)
    ReasonForResting = 5    Too low power and Vbatt below set point for 90 seconds
    ReasonForResting = 6    FETtemperature >= 100C Hot
    ReasonForResting = 7    Ground Fault
    ReasonForResting = 8    Arc Fault
    ReasonForResting = 9    (IbattDisplaySi < -15) (negative current) (MB 4200)
    ReasonForResting = 10   (dispavgVbatt < LBDlowV)  Battery less than 8 Volts
    ReasonForResting = 11   Vpv >= 90% of Voc but slow. Low Light #1
    ReasonForResting = 12   Vpv < 90% of Voc   Low Light #2
    ReasonForResting = 13   Vpv > (Voc + 10V) in    PV_Uset || Solar1_OandP
    ReasonForResting = 14   Vpv >= 90% of Voc  but slow.  Low Light #3
    ReasonForResting = 15   Vpv < 90% of Voc and taking too long.  Low Light #4
    ReasonForResting = 16   Normally because user turned MODE OFF...  Disabled
    ReasonForResting = 17   Vpv > 150V  (classic 150)
    ReasonForResting = 18   Vpv > 200V  (classic 200)
    ReasonForResting = 19   Vpv > 250V  (classic 250)

    ReasonForResting = 22   Average Battery Voltage is too high above set point  (RestartTimerms = 2 sec)

    ReasonForResting = 25   Battery breaker tripped  (Vbatt shot up high)
                            (If RFR = 25 on Wakeup, check modbus register 4200)

    ReasonForResting = 26   Mode changed while running, Vabsorb raised more than
                             10.0 Volts or Nominal Vbatt changed by modbus command
                             AND MpptMode was ON when changed...

    ReasonForResting = 27   bridge center == 1023  (R132 might have been stuffed old units)
    ReasonForResting = 28   NOT Resting but RELAY is not engaged for some reason
    ReasonForResting = 29   ON/OFF stays off because WIND GRAPH is insane
    ReasonForResting = 30   PkAmpsOverLimit (will change somewhat 1-23-2013)
    ReasonForResting = 31   AD1CH.IbattMinus > 900   (peak negative battery current)

    ReasonForResting = 32   Aux 2 Logic input is high.  Aux2Function 15 (external disable/enable)
    ReasonForResting = 33   OCP in a mode other than Solar or PV-Uset (1-10-2013)
    ReasonForResting = 34   AD1CH.IbattMinus > 900 Classic 150,200 newer than 1-23-2013
    ReasonForResting = 35   Vbatt < 8.6 V  (LOW LOW battery)
    ReasonForResting = 36   Battery temperature is Greater than reg address 4161 specified
    ReasonForResting = 38, is the new sleep because "other charging sources appear to be active"
    ReasonForResting = 136  Battery temperature fell below MB reg. 4161 - 10 C (Classic turned back on)


    ReasonForResting greater than 100...  100 + PowerOnReset, WDT, etc...
    ReasonForResting = 104  Watchdog WDT reset (only at boot until first RFR)
    ReasonForResting = 111  Normal Power up boot (only at boot until first RFR)

                 [ 100 +   1 = POR,  2 = Ext. Reset  4 = WDT  8 = Brown Out ]

   ..."
FWIW.   Mods,   please change/move this to its rightful place  if needed.   Thanks,  Vic
« Last Edit: December 29, 2016, 08:56:46 AM by TomW »
Off Grid - Two systems -- 4 SW+ 5548s, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 3X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  Thanks MN for Great Products/Service/Support!

2twisty

  • Jr. Member
  • **
  • Posts: 72
Re: Reason For Resting - RFR Table (from a boB post)
« Reply #1 on: December 01, 2014, 12:46:34 PM »
Can you add to that post how you retrieve that information from the MNGP?

Halfcrazy

  • Hero Member
  • *****
  • Posts: 2387
Re: Reason For Resting - RFR Table (from a boB post)
« Reply #2 on: December 01, 2014, 01:49:58 PM »
I modified the post
Changing the way wind turbines operate one smoke filled box at a time

eyeinthesky

  • Newby
  • *
  • Posts: 12
Re: Reason For Resting - RFR Table (from a boB post)
« Reply #3 on: December 09, 2015, 05:42:33 PM »
I'm getting a 38:Unknown on a classic 150, anyone know what that one is?  I did not see it in the above list.  Thanks!
If common sense was so common, why doesn't anyone have it?

zoneblue

  • Hero Member
  • *****
  • Posts: 964
Re: Reason For Resting - RFR Table (from a boB post)
« Reply #4 on: January 30, 2016, 02:09:07 AM »
Bob clarified just the other day that 38, is the new sleep because "other charging sources appear to be active" and the classic is no longer required. ie something is holding the bank above teh classic setpoints. You might also see this after a bank transits from EQ back to float.
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

Resthome

  • Hero Member
  • *****
  • Posts: 1149
Re: Reason For Resting - RFR Table (from a boB post)
« Reply #5 on: January 30, 2016, 03:37:17 PM »
I'm getting a 38:Unknown on a classic 150, anyone know what that one is?  I did not see it in the above list.  Thanks!

ZB is correct. Here's boB post

http://kb1uas.com/mnsforum/index.php?topic=2880.msg27522#msg27522
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

mike90045

  • Hero Member
  • *****
  • Posts: 736
    • The Ranch (via facebook re-direct)
Re: Reason For Resting - RFR Table (from a boB post)
« Reply #6 on: December 29, 2016, 03:15:46 AM »
#38 unknown

So, could the table be updated to include #38 ?
  That would simplify future searches
(I just started getting #38 this last week, cold temps pushed my other controller into higher voltages)

 Thanks
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

TomW

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 1415
  • Nullius in Verba
Re: Reason For Resting - RFR Table (from a boB post)
« Reply #7 on: December 29, 2016, 08:59:18 AM »
#38 unknown

So, could the table be updated to include #38 ?
  That would simplify future searches
(I just started getting #38 this last week, cold temps pushed my other controller into higher voltages)

 Thanks

I updated the table with    ReasonForResting = 38, is the new sleep because "other charging sources appear to be active" . Hope it helps.

Tom
« Last Edit: December 29, 2016, 09:01:15 AM by TomW »
Do NOT mistake me for any kind of "expert".

( ͡° ͜ʖ ͡°)


24 Trina 310 watt modules, SMA SunnyBoy 7.7 KW Grid Tie inverter.

I thought that they were angels, but much to my surprise, We climbed aboard their starship and headed for the skies

mike90045

  • Hero Member
  • *****
  • Posts: 736
    • The Ranch (via facebook re-direct)
Re: Reason For Resting - RFR Table (from a boB post)
« Reply #8 on: April 19, 2017, 02:56:46 AM »
In the same system, most days, my classic goes to rest  with reason #4,  but sometimes #5
    ReasonForResting = 4    dispavgVpv < (dispavgVbatt - 10) Now -25 (RestartTimerms = 1500)
    ReasonForResting = 5    Too low power and Vbatt below set point for 90 seconds

These are readings late evening, sun has been down for several hours..   What is the Vbatt setpoint ? The system battery voltage?
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV