Over current trip due to inrush current

Started by Aussierob, July 12, 2015, 12:23:30 AM

Previous topic - Next topic

Aussierob

Hoping someone may have an answer. I have a new Kid that will be installed in a remote cabin. I am testing it at home. To simulate the LED lighting load it will have, I have three MR16 lamps that draw 11.2Amps when on. I am finding that when the Kid reconnects after a low voltage disconnect, It immediately turns off the output and displays the "over-current" fault. The amp limit for the load is set to 30 amps. Does anyone know if the Kid is sensitive to inrush currents? If I disconnect one lamp, it will turn on the remaining two without problem, but it won't switch on three.

Thanks for any info.

Rob :-)

Vic

Hi Rob,

There are many different MR16,  now.   But assume that these MR16s that you are using are incandescent,  and that is why you asked about Inrush current.

Many incandescent lamps have very large inrush currents -- up to 10X the operating current,  perhaps more.

If I were a KID,  I would be sensitive to any overcurrent situation,  but do not use the Load terminals on the KID here,  so cannot respond to your question directly.

If you had a resistor that you could place on the Load terminals,  that would simulate the approximate load that the real LED lighting demands,  you could measure the voltage,  or perhaps place a small LED lamp,  with suitable current-limiting resistor to get an idea of how the Load function will behave when you have the real LED lights as a load ...   FWIW,  Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Aussierob

Thanks Vic. I know I could test it out, I am hoping someone (maybe a midnite solar someone) who has been through this can provide some insight. Maybe tested it on various loads and knows what it will and wont do.

Thanks.   :)

mike90045

If you are running enough LED lighting to need a 11.2A dummy load, you also better invest in sunglasses.

But seriously, 11A is enough to cause a noticeable voltage drop at 12V because you better spread that 11A of lighting out over a large area.

What happens if you switch on one lamp at a time, can you get all 3 lit eventually ?
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Aussierob

Have my sunglasses   8)   I am installing 13 LED lamps in a backcountry cabin so lots of spread. The system will happily turn on two of the MR16's but not three. In my real world application the lights will be on three circuits so I'm not worried about them all being turned on at the same time. I think in my application I'll be fine, but I could imagine someone with a 20-30 amp load having issues. It may be a filter or delay needs to be programmed in the firmware to allow an inrush. Of course the easy way out is to use a relay, but that adds complication, and one of the reasons to use a kid is that it has load switching built in.

Rob  :)

Westbranch

Are you running them off an inverter or 12 V?  Most MR (all?) are 12 v lights including the LED versions.. it it's a cabin go native....12 v that is...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Aussierob

No inverter in this system. Everything is 12v.

Westbranch

#7
Ouch, that is ~ 50 W rating per LED, we had 3 @ 4 w, 12V native, MR16 LED lights in our old 512 Sq ft , 16' x 32' cabin and had oodles of light, it must be like an operating room in there...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Aussierob

No 50w LED's. I have some 35w and 50w MR16's as dummy load for testing. In the cabin we will have 13 5w LED lamps, all spread out.

Bunkie314

How about just turning on/off a 12V relay with the kid load terminal and connect the load to the battery? Fairly simple resolve with higher amp capacity if so desired. Don't forget to the fuse the relay feed.
10-ePVL 136w unisolar panels, 3-lifeline 4D AGM batteries, 2012 Magnasine inverter/charger and two kids on mobile app.

30 Solartech 305w mono awaits remote cabin install

Aussierob

Hi Bunkie,
I could do that, but it kind of defeats the purpose of having a controller with the switching built in. I'm pretty confident that my application will be fine, given there will be three circuits of load at about 2 amps each. It's not possible to switch them all on at the same time.

Rob :)