Author Topic: After upgrade Advice and Help on 1344 Watt PV / 24 volt System  (Read 1352 times)

Robin

  • Hero Member
  • *****
  • Posts: 541
Re: After upgrade Advice and Help on 1344 Watt PV / 24 volt System
« Reply #15 on: January 30, 2016, 12:42:46 PM »
The guys here have given you excellent advice. They are to be commended.
Robin Gudgel

cpttom

  • Newby
  • *
  • Posts: 18
Re: After upgrade Advice and Help on 1344 Watt PV / 24 volt System
« Reply #16 on: January 30, 2016, 10:49:19 PM »
Howdy Mike,
Thanks for asking. Had to add a little water to all the batteries.  Seemed like normal amount considering that it was month and a half since the last time I topped them off when I shut down the cabin.

What was the water level after the long absence ?      Water usage is a fair indicator of if you are charging enough.

   If you had to add none or a little water, you are good as is.

  If you had to add a lot, I would dial back the charging some.
System: 1344 Watt PV Array (2x3 Sharp 224 Watt ND224UC9BX panels) | Midnite Classic 150 w/WBjr| Schneider Electric Conext SW 2524 Inverter, with SCP and Combox| 2x4 6v 235AH Duracell EGC2 Batteries @ 24V, 470 AH|  7 KW propane generator