Dirty environment.

Started by McHero, January 13, 2016, 10:18:56 PM

Previous topic - Next topic

McHero

My house batteries are in the left rear compartment open somewhat to the road. Can get dirty, sandy and dusty. I'm wanting to install a WBJr BUT was wondering if that little circuit board that screws to the shut will get dirty & fail?

Thanks

Robert
2007 Fleetwood Discovery 39V
1 255W panels, Classic Light 200, Xantrex Freedom inverter, 400ah 12VDC battery bank, Onan Quiet diesel 7K, Onan Energy Command 30

Westbranch

What options do you have to move the shunt into the interior of the coach..? 
Electronics, road dust/dirt do not mix well!  :o
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

McHero

Id have to run a good 3 to 4 foot cable each way. Might have to pass on the WBjr and get a seperate Battery monitor. The ones I have used B4 don't have a board on the shunt.

2007 Fleetwood Discovery 39V
1 255W panels, Classic Light 200, Xantrex Freedom inverter, 400ah 12VDC battery bank, Onan Quiet diesel 7K, Onan Energy Command 30

Westbranch

I only has top be the negative that is used.. I have used an XBM from Xantrex in the past and now the WBjr, the latter being far more useful...  :)
best of all it lets you use a 'real' EndAmps' setting to terminate absorb stage, otherwise you are just guessing at the completeness of that charge stage.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

Hi McHero,

That WBjr circuit board comes with a  plastic cover over the top.  You could add an additional plastic cover over it.

Doubt if that would be an issue for the WBjr as provided by MidNite...   why not try it,  as it?

The WBjr is far less expensive than is another battery monitoring/current sensing device,  AND,  the WB teams with the Classic,  allowing EA based on battery charge current.

FWIW,     Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

mahendra

You can try putting it in one of those plastic junction boxes for added protection if not it's very simple to make  a mini clear one from plexiglass and silicone similar to fabricating an aquarium.Just a thought.
1.5kw on Midnite classic 150(whizbang jr.) networked 0.660kw on classic lite 200 ,180ah CALB Lifepo4 48v battery bank,123SmartBMS bms(top balanced) Outback vfx3648

TomW

It has been awhile since I installed mine and I am no where near it to check. I seem to recall that the board has a conformal coating so, with the plastic cover and sealed board it should handle crud up to a point.  Getting wet will be the real problem as moisture can penetrate most things and especially terminals and connections. Terminal grease can help with moisture penetration and I use it on most connections now.

Maybe One of the Midnite guys will comment.

Just my opinion, likely not shared by everyone.

Tom
Do NOT mistake me for any kind of "expert".

( ͡° ͜ʖ ͡°)


24 Trina 310 watt modules, SMA SunnyBoy 7.7 KW Grid Tie inverter.

I thought that they were angels, but much to my surprise, We climbed aboard their starship and headed for the skies

Halfcrazy

I think it would be fine, As long as it doesn't get physically wet I think you are good to go
Changing the way wind turbines operate one smoke filled box at a time

zoneblue

Or else the battery cable must eventually go somewhere more civillised to where the CC is... Can you put it there? Personally prefer to keep all the high current capable stuff inside the disconnect.
6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

CDN-VT

OR !!!!!!!!!!!!
Use #10 Gauge wiring & clean connections & use the wire to move the the WBJr to a cleaner spot!!!
It's just a 50mv drop & the WBjr will be close enough to accurate rate for the kid / classic ..
Just make sure you get the wire on the correct side for the WBJr and in photos , & they give you the screws .

I myself would use Stablaint 22 or SDG on all connections , but that's getting amal ..

Just do a good remote mount !

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

CDN-VT

Here is a Tri-Shunt setup !
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

McHero

Thanks for all the suggestions! Currently working to replace the bats then i'll install a WBjr. Looking at wet cells so I'll be cleaning them monthly!
2007 Fleetwood Discovery 39V
1 255W panels, Classic Light 200, Xantrex Freedom inverter, 400ah 12VDC battery bank, Onan Quiet diesel 7K, Onan Energy Command 30

mike90045

Since the shunt is a precision resistor, what is the heat dissipation under full rated load ?

Will enclosing it in a plastic box cause a problem?
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

brad.midnite

A 50mV/500 Amp shunt has a resistance of R=V/I, or 100 uOhms (micro-Ohms).

The power dissipation in the shunt is most easily calculated by using P = I^2*R. So to find the power dissipation in Watts, multiply the square of your current by .0001

Example:
P = 100^2*.0001 = 1 Watt
P = 500^2*.0001 = 25 Watts

So it really depends on your usage. 25 Watts can produce significant heat in a small case. Larger cases will do a better job of dissipating heat due to their larger surface area.

From the shunt manufacturer:

For continuous operation, it is recommended that shunts are not used at more than 2/3 of the rated current under normal operation conditions. Shunts should be located in an area where freely circulating air is available. If this is not possible adequate forced ventilation should be provided to keep the shunt operating temperature at -40° to +60°C. Shunt temperature must be maintained under 145° C or a permanent change in resistance will occur.

russ_drinkwater

If heat is not an issue with the WBJ then you could screw a small clip on lid type food container near your batteries.
The WHJ could be mounted inside it with 3 holes to allow cable access and then silicone the holes for a good dirt proof job.
Clip your lid on to finish the job. Also if you use a transparent one you can still see the 5 second led pulse.
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters