OK so I'm adding the SPD 115v to the output side of my classic charge controllers. Pic of my setup.

Wide Shot:


Close up:


I plan on having it in between the fuse holders (Blue and white) after I move them further apart. Or possibly either side of the fuse holders. What do you think would work best?

Now to stop a lightning induced surge from damaging the classics I assume the SPD wires must be shorter than the length of wire to the classic controllers. Is that correct?

Westbranch

Do you have SPDs on the combiner box, by or at the Array?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

zoneblue

Generally speaking the battery will serve as a pretty good surge isolator. The input to the classic is more vulnerable, as is the inverter output /and/or AC input. The SPD acts by conduction overvoltage between the active leads and the ground (hence source) lead, so keeping them short, with miminal bends is wise.