Breakers size, orientation and wiring?

Started by sigp2101, March 01, 2016, 01:35:56 PM

Previous topic - Next topic

sigp2101

All I could read up to now points me that breakers should be installed between:
PV array and Controller,
Controller and Battery Bank,
Battery Bank and Inverter.

Questions I am struggling with are as follows.
Size in Amps and Voltage for each breaking point,
+ and - orientation,
cable hook ups, breakers will not accept required wire size.

Here is my off grid system description:
3 X 235W 36V 8A PV in parallel,
Midnite Classic 150 controller,
12V 6 X 6V Battery Bank. Inverter is yet to be determined but it will be no bigger then 1000W.
Already have Junction box with 3X15A breaker on each wire going in to serve as disco.

So, will all this info be sufficient enough to provide some suggestions? Appreciated.
Off grid system:
3 X 230W 36V 8A SolarWorld in series,
Classic 150,
36V BB - 225Ah 6x6V Trojan T-105 T2,
3000W psw Inverter,
Fridge 159KWh/Y, 30W led lights, laptop, TV.

Westbranch

have you seen this diagram, it needs another panel, ++ but you get the idea..

http://www.midnitesolar.com/pdfs/Kid_12V_2p_Par_REV_B.pdf

You NEED to tell us more before we can get started..
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

sigp2101

#2
Quote from: Westbranch on March 01, 2016, 02:05:34 PM
have you seen this diagram, it needs another panel, ++ but you get the idea..

http://www.midnitesolar.com/pdfs/Kid_12V_2p_Par_REV_B.pdf

You NEED to tell us more before we can get started..

Interesting, what I need to know is how they come up with those values 15A and 30A for the breakers.
Typically those panels would be around 6A each. When you bring them down to 12V from 36V as shown they will be almost tripling amperage.

What additional information community needs to know? I will be glad to answer.

Thank you!
Off grid system:
3 X 230W 36V 8A SolarWorld in series,
Classic 150,
36V BB - 225Ah 6x6V Trojan T-105 T2,
3000W psw Inverter,
Fridge 159KWh/Y, 30W led lights, laptop, TV.

ClassicCrazy

You size the PV input breaker for the size wire you are using . Same for the breaker size for output to the battery.

Of course you are limited to the amps that the controller is capable of  so  for example if you had a controller that only could do 15 amps you could use 12 gauge wire and a 15 amp breaker. But in the real low voltage world you have to consider voltage drop so you use larger gauge wire - so lets say you used 10 gauge wire you would have to use 30 amp breaker ( sized for the wire ) even though it was only 15 amp load on it.  Those are just generalizations but hopefully you get the idea.

My first setup with 24v battery system had 63 amp input breaker because I had 6 gauge wire in. I had to up the output to the batteries up to 100 amps since the Classic is capable of charging 90 some amps at 24v .  I had a 63 amp breaker on battery output at first but it tripped a few times so I upped it to 100 amp.

So you need to know how far you will run your wiring so you can determine voltage drop in order to decide what size wire you need. And use the Midnite string calculator or other calculators online that will give you all the voltages for your particular system.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

zoneblue

Quote from: sigp2101 on March 01, 2016, 01:35:56 PM
Here is my off grid system description:
3 X 235W 36V 8A PV in parallel,
Midnite Classic 150 controller,
12V 6 X 6V Battery Bank. Inverter is yet to be determined but it will be no bigger then 1000W.
Already have Junction box with 3X15A breaker on each wire going in to serve as disco.

You have the right idea. If you think about the battery positive being a bus, and EVERYTHING that is connected to it having a breaker, youll do fine. (Dont forget to ground-bond the DC negative though).

PV: this breaker is more of a switch as the PV is current limited. Make it more than the combined Isc by at least 25%, and assuming your wire guage is big enough to limit voltage drop to 5%, youll be good to go there.

CC: this one is important, take your peak charge rate (45A), go to the next size up, or one more if its close (60A). If its a CBi orient it so that the positive(line) is to the battery. Then size that cable so that a voltage drop of under 0.2V occurs. This is much more important than teh PV drop, as it dictates charge setpoints. Double check the ampacity to be sure.

Inverter: You want the voltage drop low there too, to stop the inverter dropping out on surge. 0.2V is cool there too. The breaker is sized to peak discharge (100A), next size up. So 125A. Thats an issue because that puts you into a Carling, which are big, cost more and require a step up from Big Baby to MNDC.

Are you sure you would rather goto a 24V system? Then you can use a 60A for the inverter breaker.

You also need 3 breakers to combine the three PV modules. You can use a 3 slot combiner and some Cbis there for that, set at the nameplate fuse rating.

For the drops hit the calculator:http://www.calculator.net/voltage-drop-calculator.html


6x300W CSUN, ground mount, CL150Lite, 2V/400AhToyo AGM,  Outback VFX3024E, Steca Solarix PL1100
http://www.zoneblue.org/cms/page.php?view=off-grid-solar

russ_drinkwater

Zoneblue, why do you need breakers to combine the 3 PV modules?
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

Westbranch

Russ it is protection for any of the 3 panels should there be a back-feed issue, 2 could back feed a third and there is a possibility of a fire.... needed when > 2 panels are combined...  the amperage for the CB is shown on the back of your panels, or should be...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

russ_drinkwater

One amperage is 8 and the other in the specs is 8.5 amp.
I only have 2 panels combined (series) which gives me 58-59 volts for a 24 volt system.
But there are 4 lots/strings (parrallel) of 2 if that's what you are talking about.
No mention of circuit breaker on the back of the panels unless I am missing something.
And that of course happens to me! ???
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

Westbranch

here is the spec sheet for one of my old PVs, attached, see page 2 for breaker size, called FUSE rating


you use ISC * 1.25 *1.25 and go to not highest CB rating
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

russ_drinkwater

Yep, had another look at the specs on the back of a panel.
There is nothing even remotely similar to fuse rating listed.
I will have to do a newt search for further specs. :o
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

Resthome

Quote from: russ_drinkwater on April 05, 2016, 02:24:05 AM
Yep, had another look at the specs on the back of a panel.
There is nothing even remotely similar to fuse rating listed.
I will have to do a newt search for further specs. :o

They show a Maximum Reverse Current of 15A on their Data Sheets
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

russ_drinkwater

So i should be right with only 2 panels?
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

Westbranch

2,3,4 or more in a string (series) all have the same amperage as one panel,  only the voltage increases, it is in parallel that you need the circuit protection from any of the other strings backfeeding / (Maximum) Reverse Current
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come