Started by Powerplay, May 18, 2016, 11:13:14 PM

Previous topic - Next topic

Powerplay

I don't if this is the correct place to ask.  I'm running my battery charging from the controllers through a 2 AWG cable and it is protected by a MNEDC100 (100 amp panel mount) breaker.  Does MidNite make a 120 amp version of this breaker which would better match my wire and fit the same space on the panel?  Otherwise, I'll have to start limiting the Classics later this year when I have over 3 Kw put out.  These Mono-Crystals have been getting close to 90% lately.  I figure a 120amp could cover 4000W X 85% / 28V. and the wire handles that with ease.
41 degrees N, 255 Ah 48V AGM, MagnaSine 4448 Inv, 3500W PV, Midnite Classic 150 A (12/6/15), Midnite Classic 150 B (4/14/16), WBjr, BTS, MNPV6 X 2, SPD X 2, Apps: Mini Split AC, Car Charger, Water pumps, Lighting, -> 48V string plan 500W, 94.5VmP, 112.5VoC, -15C - 40C TCVoC -.3%, TCIsC +.04%

Westbranch

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

Quote from: Powerplay on May 18, 2016, 11:13:14 PM
...     Does MidNite make a 120 amp version of this breaker which would better match my wire and fit the same space on the panel?  ...   

Hi Powerplay,

Quick answer is NO.   100 A is the maximum Rating for this size breaker  --  it is a C-Frame size.

The MNEDC125  is an E-Frame breaker (IIRC),  physically,  it is MUCH larger.   The E-Frame breakers will not fit in the MNDC Quad boxes,  or any other place that the C series breakers fit.

If you are using an e-Panel,  there may be a spare spot for an E sized breaker,  but  doubt that there would be two unused positions for these large breakers.

And,  know of no smallish electrical boxes that are designed for and Rated to accept several E series breakers.

FWIW,    Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

tecnodave

Powerplay,


Read the ratings for the Classic.......it's 84 amps at 24 volt battery bank...at 28.8 volts that's about 2700 watts......(that's Assuming you have a Classic 150....the higher voltage ones are less current)....are you trying to cook your controller?......be a bit more conservative, it will last a lot longer....I run a maximum of 2kw into each of my two Classics and 560 watts in each of my Kids, I don't like my electronics running so hot.

I set my maximum current out of the Classics at 75 amps and use MidNite MNEDC-100 amp breakers on each one

David
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P