Multiple measurements off one shunt

Started by asdex, July 31, 2016, 11:23:17 PM

Previous topic - Next topic

asdex

Hi, having trouble finding info on this.
Can I take another current measurement from the same shunt the WBJr is connected to?
Cheers,
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North.
12 x 2volt Narada lead carbon batteries (24v 400ah), Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Trimetric monitor, Alibaba solar pump.

Vic

Quote from: asdex on July 31, 2016, 11:23:17 PM
Hi, having trouble finding info on this.
Can I take another current measurement from the same shunt the WBJr is connected to?
Cheers,

Hi asdex,

YES !!  Most instruments that use these 50 mV 500 A Shunts are fairly high impedance,  and that Shunt has a profoundly low impedance.

If that makes sense,  so to speak.   Good Luck,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

CDN-VT

yes , as the second / third  must use the 50 MV style of shunt .
use stand offs , I would have WBjr closest , then the the meters after that or further away from the shunt.

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.