jmarc

Hi,

I'm looking for a wire lug to connect from a charge controller to a mne175sw breaker. The wire is 6awg thhn. Any recommendations?

Vic

Hi jmarc,

As you probably know,   breakers are used to protect wire and cable.

A 175 A breaker should probably have 2/0 cable connected to it.   Assume that this breaker is in a MiniDC,  or e-panel.    If so it is more difficult to simply replace the 175 with a breaker that has an appropriate rating for 6 AWG cable   ...   IMO.

Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

jmarc

#2
Hi yes.  Actually from charge controller to 60amp breaker then to175amp breaker.  Both the charge controller and battery connections will land on the 175amp breaker.

Vic

#3
Quote from: jmarc on December 11, 2016, 08:05:35 PM
Hi yes. Both the battery and charge controller will land on the breaker.

OH!  OK.   So the cable from the battery to the breaker,  and from the breaker to the inverter will be 2/0 or larger?

And,  the #6 AWG cable from the CC to this 175 A breaker will have a breaker that has about a 60 amp rating?   If so,  this would be fine.

You could use a 3/8" ring terminal on the #6 cable,  and use the 3/8" bolt that is on the breaker.   It might be difficult to find a screw lug that has a clearance hole for the 3/8" bolt on the breaker terminal.   They are probably available,  but perhaps not in the big box stores.   It might be OK to drill the hole in the screw terminal lug for a 3/8" bolt.

Sorry for my confusion on exactly what you were doing.

FWIW,   Vic

Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

jmarc

I found an image from a midnite manual of the stacked connection. See attached. Where can i find a ring terminal similar to that? I tried looking at the big box stores with no success.

Westbranch

Automotive stores , like NAPA... up here, have the best selection of tinned copper connections.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

jmarc

Thanks! Im a bit weary about using the vinyl insulated ring terminals, but the second link looks similar to the one on the image. Thanks!

Do you recommend the tin plated terminals or copper?

Vic

jmarc,

Would always use Tin plated,   almost without exception.

BTW,   many crimp terminals at Auto Supply stores  are Tin plated,  but,   often the Tin is on a steel terminal ...   steel is not a good base metal for electrical terminals,  IMO.

Good Luc,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

jmarc

Thanks Vic for you help! Any recommendations on which crimper to use on the marine lug?  I have a green lee k111 but not sure if its compatible.

CDN-VT

Go into a NAPA or an electrical supply house .
I buy them in boxes , But napa sells them in pairs .
They come in swedge  or CRIMP or Solder . They do have 3 types .
look into beldon / pico .
They are in stud hole size & wire AWG size . I have made a few from

They are in 0-10 AWG size  & I drill a hole & re-tin if need be . For long distance runs

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

solar blue

       Cdn vt what did you make lug conecttor out of
trying to wrap my head around this

Resthome

Quote from: jmarc on December 11, 2016, 10:06:05 PM
Thanks Vic for you help! Any recommendations on which crimper to use on the marine lug?  I have a green lee k111 but not sure if its compatible.

Not Vic. But I would recommend taking to Ancor they have various crimper for their marine lugs. And their HD lugs are 100 percent heavy-duty annealed tinned copper.
John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

CDN-VT

Quote from: solar blue on December 27, 2016, 08:47:36 PM
       Cdn vt what did you make lug conecttor out of
Let me find one & take a picture.
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels