Quote from: Westbranch on November 26, 2016, 07:44:20 PM
was just looking at the  REDFLOW site and they now have several inverters that will work for their power 'cells',...   

In the last month, I've been in contact with their CEO (who I knew from a previous life in the ISP game), seriously considering going that route.

Wow, what a disappointment.

They're built on 10kWh modules, and when they say they'll always have the full 10kWh capacity, what is less obvious is that you need to put around 12.5kWh into them (new) and up to 14kWh or so, after their rated number of cycles. So cycle efficiency is fairly low.
Also, you cannot just "add more electrolyte and bigger tanks" for longer run time. They don't work like that, they're a hybrid flow cell. Basically, you use power to deposit zinc onto plates to "charge", and then recover that power by returning zinc to the electrolyte. The capacity is therefore more "how much zinc you can fit on the plates".
Next was the relatively low charge and discharge rates. A maximum sustained charge or discharge rate of 2.5kW, I think peaking to 3kW.
Now for the two real deal-breakers....
A non-optional "maintenance" cycle where the cell must be completely discharged and the plates cleaned. While this is automatic and doesn't require manual intervention - it does mean that every (roughly) 100-120 hours of operation, you're going to be offline for somewhere between 40 mins and several hours. So you're going to want grid backup, or generator backup, or another cell (assuming 2.5kW is enough for your needs).
And the price of around $13,000 for the cell alone (around $19,000 with all its bits and bobs), no DIY - must be one of their approved people, and basically a 12-month guarantee.

They're also heavy (compared to lithium, but not so heavy as lead) at around 250Kg (550lbs) for  a 10kWh cell, and they need a ventilated area.

If you've got millions of dollars of investor money and you're building the fanciest site out of all the coolest bits you can find... sure. But for most of us they are just far too expensive and have far too many downsides.
3600W on 6 tracking arrays.
7200W on 2 fixed array.
Midnite Classic 150
Outback Flexmax FM80
16 x LiFePO4 600AH cells
16 x LiFePO4 300AH cells
Selectronics SP-PRO 481 5kW inverter
Fronius 6kW AC coupled inverter
Home-brew 4-cyl propane powered 14kVa genset
2kW wind turbine

Westbranch

Hi Ross, I had a few emails with them a few years ago and another point they made was that if you need more power than the unit can deliver in a set amount of time, think AGM dumping its power 'NOW!', you would probably need a separate bank of lead batteries that you slowly recharge from the RedFlow.... redundant duplication ...??? why 2 banks vs 1... ?

We should probably start another thread , so as to stay on topic,  Tom??
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

TomW

Hope this topic split off was accurate, I did not find the original Redflow post quoted by Ross.

Golly, only a couple more days til the days start getting longer! Can't make much Solar power in 9 short sun hours and 30% of that being shaded.

Seasonal type best wishes to everyone and hope you are healthy and happy.

Tom
Do NOT mistake me for any kind of "expert".

( ͡° ͜ʖ ͡°)


24 Trina 310 watt modules, SMA SunnyBoy 7.7 KW Grid Tie inverter.

I thought that they were angels, but much to my surprise, We climbed aboard their starship and headed for the skies

RossW

Quote from: Westbranch on December 18, 2016, 06:14:36 PM
Hi Ross, I had a few emails with them a few years ago and another point they made was that if you need more power than the unit can deliver in a set amount of time, think AGM dumping its power 'NOW!', you would probably need a separate bank of lead batteries that you slowly recharge from the RedFlow.... redundant duplication ...??? why 2 banks vs 1... ?

Well, if you're trying to get away from all the downsides of lead-acid, it seems utterly inconcievable to me that you'd then add another lot just to provide for all the shortcomings of the uber-expensive flow-cells!

Even the zcell doesn't have an infinite life - and if you amortize its cost over its expected life, it still doesn't stack up well against other "well known" technologies like lead-acid (flooded or agm) or LFP.
3600W on 6 tracking arrays.
7200W on 2 fixed array.
Midnite Classic 150
Outback Flexmax FM80
16 x LiFePO4 600AH cells
16 x LiFePO4 300AH cells
Selectronics SP-PRO 481 5kW inverter
Fronius 6kW AC coupled inverter
Home-brew 4-cyl propane powered 14kVa genset
2kW wind turbine

Westbranch

Exactly, my closing line there was meant to show my puzzlement of having a bank (AGM) that gives me what I want supported by a bank (RedFlow) that does NOT serve me well... and now I see it has very poor efficiency...  I guess it is best suited to the Oz outback... lots of sun, maybe too much for us... and above freezing temps most of the time 99.98% ;)...

LiFePo4 would be a lot better choice as it has FLA capabilities to serve large loads and not have to reach Float regularly  (or ever?).
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

RossW

Quote from: Westbranch on December 19, 2016, 01:29:33 PM
LiFePo4 would be a lot better choice as it has FLA capabilities to serve large loads and not have to reach Float regularly  (or ever?).

Yes, this. 2 years ago I replaced my aging, second-hand AGM (2 x 500AH banks) with a 300AH LiFePO4 (LFP) bank.
Our dollar was very good then, and that only cost me $5K, however on every metric I have, this new bank outperforms my old 1000AH storage. It's stiffer, it soaks up current effortlessly, it has higher cycle efficiency, it handles transients better, its output voltage remains almost constant. On top of that I replaced over 1.6 tonnes of lead-acid batteries with a mere 370 lbs of LFP (so 90% lighter) and the new bank fits in less than 1/4 the space of the lead! The LFP cells have not demonstrated any memory effect, don't seem to get "lazy" when not fully charged and floated (or when they HAVE been!)...

I need additional capacity now because of some additional base load that I'm adding. It will be LFP, not zcells.
3600W on 6 tracking arrays.
7200W on 2 fixed array.
Midnite Classic 150
Outback Flexmax FM80
16 x LiFePO4 600AH cells
16 x LiFePO4 300AH cells
Selectronics SP-PRO 481 5kW inverter
Fronius 6kW AC coupled inverter
Home-brew 4-cyl propane powered 14kVa genset
2kW wind turbine

grgdgreek

Home:6*135w mitsu.10*175w shuko. 2* cl150.3*D400 turbines.
Rolls18*4v series 5000 545ah*3 .2*Victron 3000 multiplus inv/chg. 24v. Shop:28*185w shuko. Sunny island. Sunnyboy.Rolls 40*s530.48volt.Sunny web box.

RossW

Quote from: grgdgreek on December 19, 2016, 03:11:40 PM
What brand lfps are you using?

They were made by a company in China called "High Power", but they seem to have disappeared. Their old website still exists, but no replies to email, their old phone numbers are disconnected or re-assigned...

Here's one:


And here's them all unpacked, but before they were installed.
3600W on 6 tracking arrays.
7200W on 2 fixed array.
Midnite Classic 150
Outback Flexmax FM80
16 x LiFePO4 600AH cells
16 x LiFePO4 300AH cells
Selectronics SP-PRO 481 5kW inverter
Fronius 6kW AC coupled inverter
Home-brew 4-cyl propane powered 14kVa genset
2kW wind turbine