Shunt in SW4024 E-Panel

Started by Horsefly, January 24, 2017, 01:41:05 PM

Previous topic - Next topic

Horsefly

Does anyone know if you can swap out the existing shunt in the E-Panel for the Schneider SW4024 inverter?  I'm wanting to use one of several ammeters available on E-Bay or Amazon, but they wall want a 75mV shunt. I'm sure the existing 500V/50mV shunt will not give me correct readings. I'm away from the E-Panel right now, but wondered if anyone has swapped out the shunt for another one.

Thanks in advance!

Steve

Westbranch

I think a search for ' Shunt'  here might give you an answer, there was a (similar?) discussion about how to use a different shunt ....  maybe by boB???
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Horsefly

Well, I did search before I posted, but I'll admit I only read the short snips that the search gave me and didn't go any further. 

Thanks. I'll go look more closely.

Horsefly

Well, nothing quite fits, bit it doesn't matter that much.  I guess I can mount another shunt in series and call it good.

Vic

Hello Horsefly,  welcome to the Forum.

A 75 mV Shunt is not common  --  50 mV and 100 mV ARE common values for Shunts.

Does the supplier of the Ammeter that you are looking at on e-bay, offer Shunts with appropriate ranges for your needs,   that would be compatible with their Ammeters?

Do you know if the Ammeters that you are thinking of using have some adjustable Scale Factor?   This  scale adjustment might allow the use of a 50 mV or 100 mV Shunt.

Vic