battery wiring or copper straps

Started by solar blue, February 28, 2017, 10:50:51 PM

Previous topic - Next topic

solar blue

      First off I want to thank everyone for helping me my system is working far better then i dreamed after heart surgey march17 I plan to put up 10 more panels Lord willing. My question is will copper jumpers give less resittance then wire jumpers I can get 1\4in by 1in copper straps 3 will be 1in longer than the other 9  just a though on improving it a little.
                                                                                     Wayne 
trying to wrap my head around this

ClassicCrazy

I don't understand where you want to use the copper strapping ? 

Are those straps insulated ? It all comes down to the resistance - so you could look up the resistance for the size copper straps you have and compare it to the equivalent size wire . There is no real gain to having less resistance after a point. Really all depends on your system - the distances , amps , voltage , etc.

You need to consider how you terminate the straps too - how easy it is to make good connections that won't oxidize or corrode. And flexibility and the quality of the insulation compared to wire.

Good to hear you are healing quickly .

Larry

system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

CDN-VT

I don't have any pictures "handy" But !

I took 1/2 copper pipe that was used & spun it in a lathe to clean it up , then used solder to tin it , rolled it flat & then drilled holes for the interconnect between FLA 6vdc batterys  . Used that for the first sets I used.

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

niel

i'm going to assume this is for your battery bank. now it would be difficult to determine just what the equivalent resistance would be for the straps given to you and i would shy away from unequal lengths unless only in series. it is important to keep a paralleled battery bank looking as one large battery so the wires should be oversized for battery interconnections. even small resistance deviations have a bigger impact on the charging and discharging of all of the individual batteries within the bank. some batteries working harder than others will fail faster. in general, one would go with at least the size of wire that goes from the bank to the inverter and as i said, an even larger gauge identical in length within the paralleled bank is desirable.

solar blue

        thanks all for the info well guess wires is the best course. seems according to sg test all batteries are charging and discharging evenly so as the saying goes if its not broke dont work on it.


                                                                 thanks yall
                                                                wayne
trying to wrap my head around this

RossW

Quote from: solar blue on March 01, 2017, 03:31:54 AM
well guess wires is the best course.

I used copper bar 6.5mm thick x 25mm wide which is equivalent to about 6/0 wire.
It worked great, never gave me a moments trouble (unlike my earlier attempts with aluminium!), and I'd do it again in a heartbeat.

3600W on 6 tracking arrays.
7200W on 2 fixed array.
Midnite Classic 150
Outback Flexmax FM80
16 x LiFePO4 600AH cells
16 x LiFePO4 300AH cells
Selectronics SP-PRO 481 5kW inverter
Fronius 6kW AC coupled inverter
Home-brew 4-cyl propane powered 14kVa genset
2kW wind turbine

Westbranch

#6
My factory made bars are tinned copper about 1/4 inch.... same as Ross'
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

niel

there's nothing wrong with using bars or straps if one knows what it is one has as you don't want to compromise the system you have on an unknown.

CDN-VT

#8
It's Called a Voltage drop & if you do one & check , All should be Grand ..
Its  a test I do when Im doing water maintenance

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

russ_drinkwater

Early standalone power systems here in australia used lead strapping to interconnect batteries.
From memory there were always corrosion issues.
The straps were approx 1 1/2 wide and 1/2 thick and made from pure lead as they were very easy to bend and twist to shape.
Most were cast up with homemade molds and had a circular section on each end with a bolt hole for connection.
They seemed to do the job, but I am unsure of losses etc.
Most systems were classed as 32 volts in those days.
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

mike90045

lead is much higher resistance than copper, but more resistant to acid than copper.  So thick lead interconnect straps could work better than corroded out copper wire.
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

CDN-VT

#11
I found a few Pix of what I built & used for the early years .
VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

russ_drinkwater

Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

tecnodave



I've been using buss bars salvaged form large commercial 3 phase power panels. Some are unplated copper but the better ones are nickel plated copper. Mine are 1.00" wide .250 " thick 250 kcmil also known as 250MCM in the electrical trades. These were salvaged from a 1930's Westinghouse 1200 amp 480 volt 3 phase power panel.
For reference "0000" or quad ott is 237,000 circular mils.  250MCM is 250,000 circular mils. Quad ott is the largest sizi in AWG (American wire gauge) from there we go to the MCM standard which is 250MCM, 350, 500, 650, 750, 900, 1000 and up. The largest I have seen is 1750MCM.

I do not know if AWG is a world standard as I only do electricity in the U.S.

I coat my busses with Ideal (brand) No-Alox , a product used here to prevent corrosion on electrical connections........Required under the National Electrical Code when joining copper wire to aluminum wire.......but stands up very well on batteries, in marine use, salt water corrosion, etc.

I am only a few miles from that big pond...the Pacific Ocean and replace a lot of corroded out panels

The worst are unplated aluminum buss "Murray" brand.......the best are Square D QO line with specified nickel plated copper buss and Seimens which are standard with copper busses

David
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P

CDN-VT

Quote from: tecnodave on April 05, 2017, 09:14:45 PM
I do not know if AWG is a world standard as I only do electricity in the U.S.

David

No AWG or whats  UL /CSA standards are NOT world wide.

I've worked in China / Russia  and other places , It's scary

VT