Is the Midnite SPD a type 1 device or a type 2 device?

Started by 5 Minutes 2 Midnite, July 14, 2017, 08:47:56 PM

Previous topic - Next topic

5 Minutes 2 Midnite

The website description lists the lineup of Midnite Solar Surge Protective Devices as a Type 1 device.

The installation manual denotes the device as Type 2.
Qty 24 Sharp 153W poly panels, Midnite MNPV6 combiner, Midnite Classic 150 charge controller, Magnum MS-4448-PAE inverter with RC50 remote, Magnum MMP Mini panel,  QTY 2 Chinese made self-contained 200 AH wall mounted LFP power banks with built in BMS

ClassicCrazy

#1
Wonder if the disagreement has anything to do with older model may have been Type 1 ?
This says they are all Type 2
http://www.midnitesolar.com/doc_prod_list.php?menuItem=products&productCat_ID=23&productCatName=Surge%20Protection%20Devices

The ones I have all say Type 2 on them .

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

5 Minutes 2 Midnite

Yeah, that shifts the preponderance of evidence toward Type 2.

I was just trying to figure out how they work. I mean the Midnite units specifically. I read through the PDFs, including Robin's nice write up. He only mentions metal oxide varistors though. I understand how those work. But is there more going inside that glass cage or are the MOVS the core? I've seen references to 'air gap' for surge protection.

Wait. I just googled the difference between type 1 and type 2. Found a UL related document here:

https://www.google.com/url?sa=t&rct=j&q=&esrc=s&source=web&cd=2&cad=rja&uact=8&ved=0ahUKEwjF5dXHp4rVAhWr34MKHQuPCKkQFgh2MAE&url=http%3A%2F%2Fwww.electrical-installation.org%2Fenwiki%2FThe_Surge_Protection_Device_(SPD)&usg=AFQjCNFeBcPf7hzNP_mpSJO1rWhPxdtRqQ

It appears type 2 devices are more restricted in their placement. Moreover, it seems type 2 devices may or may not include "external overcurrent
protection". It is not required. Which leads to the next question: Do the Midnite devices incluse such protection, and if not, why not? (I sure ask a lot of questions, don't I?)

----------------------------------------------
EXCERPT FROM PAPER:
Some key differences between Type 1 and Type 2 SPDs are:

External Overcurrent Protection.  Type 2 SPDs may require external overcurrent
protection  or it may be included within the SPD. Type 1 SPDs  generally  include
overcurrent protection within the SPD  or other means to satisfy the requirements
of the standard;  thus,  Type 1 SPDs and Type 2 SPDs that do not require external
overcurrent protection devices eliminate  the potential  for installing  an  incorrectly
rated (mismatched) overcurrent protection device with the SPD.
Qty 24 Sharp 153W poly panels, Midnite MNPV6 combiner, Midnite Classic 150 charge controller, Magnum MS-4448-PAE inverter with RC50 remote, Magnum MMP Mini panel,  QTY 2 Chinese made self-contained 200 AH wall mounted LFP power banks with built in BMS

boB


Originally the MidNite SPDs were Type 1 rated.  All type 1 means is that you can legally connect them up
to the utility side of the breaker box.  That doesn't make them any better, really.
This was because ETL assumed some things that they later had to change. 
The MOVs have internal over-current protection but not proper for that specification.

Because of this, the newer SPDs have separate over-current protection in addition to the MOVs
and they have been re-tested.  That was fun going to Boston at a facility with 1000V and
100,000 amp capability.  We only needed 10,000 amp capability.  Those tests were not
for lightning but were for abnormal overload like, if a tree falls on your house and your
120/240 VAC lines turn into a constant 480 VAC source.

There is a newer SPD spec that we also comply with but I can't remember what that
type or spec is called right now.

Just all part of the game we have to play with the NRTLs.   It's all good.

boB
K7IQ 🌛  He/She/Me

5 Minutes 2 Midnite

I suspected that the devices had been reclassified from 1 to 2 and that the paperwork hadn't caught up yet. Doesn't see to be a problem given where they are
being installed.

thanx for the clarification.