Started by Matrix, November 06, 2017, 11:11:32 AM

Previous topic - Next topic

mike90045

Quote from: ClassicCrazy on December 10, 2017, 03:26:28 PM

Yes 48v is nicer but sure ups the costs of batteries - double of 24v  system .

Larry

I disagree.   If you require 8Kwh of storage, it needs about the same amount of lead, for both 24V or 48V systems.  The 48V bank can be half the Ah of the 24V bank,  which makes the cost of either bank, about the same per wh of storage.
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

CDN-VT

Agreed

I only use 24Vdc for one system because it charges my MAN LIFT  Genie
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

ClassicCrazy

As far as cost for 24v compared to 48v it all depends on the size cells you are going to use and  if you can find ones half the amp hour capacity for half the price so you can string together the same size battery pack.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

Matrix

Wow! Being a Total Noob it never occurred to me that 48v would require half the amp hours. Makes sense. And if I would have realized this I would have gone 48v, and for just about 30% more than my 4 435ah batteries at 24v, I could have gone 8  48 v and 265ah but more capacity ? Am see this correctly?
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Bob D

Yep
24V x 435AH = 10,440 W-H
48V x 265AH = 12,720 W-H

Classic 150, Magnum 4024, 12-215W panels, 12-85-13 forktruck battery