Wondering why my charge current is so hi

Started by Matrix, November 23, 2017, 10:57:25 PM

Previous topic - Next topic

Matrix

I have a hybrid Conext SW Inverter / Charger.  The charger is run off of an incoming AC line (Gen or Line power).    It is capable of charging at 90 amps.   The batteries are Trojan L16H-AC 435 ah batteries. 

Doing some calculating,  it is my understanding that you should not charge the batteries at a rate higher than C/8 .... or about 54 amps.  And yet,  when I set the SW to charge,  and set my battery type to custom using 29.8v Bulk / 29.6v Absorb / 27v float ... when I start a charge at about a 55-65% SOC on the battery, the charger goes to Bulk and the charge amps shot up to 85+ amps. 

There is no way to control amps,  only volts in the charger.  (in the Classic 150  I could set an Amp Output limit).    I thought C/8 (54 amps)  was about the max I wanted to charge this 435ah 24v battery bank at.   If I lower the charge volts,  the batteries never fully charge as test with hydrometer.   But even if I do lower the volts the amps are still very hi.  Like about C/5.

  Help me understand what i am missing here.

Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

mike90045

isn't there a setting for battery amp-hour size?
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Matrix

Quote from: mike90045 on November 24, 2017, 12:01:31 AM
isn't there a setting for battery amp-hour size?
Yes. I have it set to the battery size... 435ah.   I guess I could lower it and see what happens. If that lowers the amps
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

mike90045

there may be interacting settings, breaker size. battery size, generator size.    Go through your manual and see if Schneider has hidden any tidbits regarding those settings.  They are pretty obtuse about them.
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

CDN-VT

@matrix
Do you have a Schneider Electric Conext XW+/SW System Control Panel (SCP) ?
under advance you will find limits on charge & steps of charging . Or Conext Combox for Network Monitoring and Remote Access with a laptop.
I have a 6848 stack that im about to commission in , but i'm needing a BTS that I might of left @ the Midnite plant .

The trick to see advance is hold 3 buttons on meters enter ,Up & Down  advance shows , that works under charge also & a few places .
Like 141 for Outback

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

Matrix

Quote from: mike90045 on November 25, 2017, 12:30:01 AM
there may be interacting settings, breaker size. battery size, generator size.    Go through your manual and see if Schneider has hidden any tidbits regarding those settings.  They are pretty obtuse about them.
Schneider is Obtuse about a lot of things.  Terrible Manual
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Matrix

Quote from: CDN-VT on November 26, 2017, 01:35:17 AM
@matrix
Do you have a Schneider Electric Conext XW+/SW System Control Panel (SCP) ?
under advance you will find limits on charge & steps of charging . Or Conext Combox for Network Monitoring and Remote Access with a laptop.
I have a 6848 stack that im about to commission in , but i'm needing a BTS that I might of left @ the Midnite plant .

The trick to see advance is hold 3 buttons on meters enter ,Up & Down  advance shows , that works under charge also & a few places .
Like 141 for Outback

VT
Hi VT,
Yes I use the Advanced settings and have the SCP and also have a battery monitor.  I am actually setting up and using the charger with Custom settings so that it is set up with the exact voltages thru the charge cycle that are called for my Trojan.  But when it starts charging the amps get really hi.  Like 90+ which is way over C/8 as recommended for the battery.   And it does this regardless if I use custom or the Flood battery type setting.

So I am going to try and lower the Amp Hour of the Battery setting to a value lower than my actual Amp Hours of 435 and see if that causes the charger to pump less amps.   
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Westbranch

Matrix, how long does the unit deliver the >90Amps? Does it not decrease over time?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

russ_drinkwater

I have not read my trojan info for a while, but isn't the charge rate of 20-40% of
rated amps the go?
If so what your charger is delivering is just a tad over recommended minimum.
If wrong I stand corrected.
The L16 trojans we have here are apparently the newer AC ones (with the carbon).
Same question as well, does the charge rate taper off after a while?
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

Matrix

Quote from: Westbranch on November 26, 2017, 01:47:40 PM
Matrix, how long does the unit deliver the >90Amps? Does it not decrease over time?
It does 90 + in the bulk stage for about 1.5 hrs.  Then yes, it tappers in absorb down from 90+ to 7.5 amps over 2.5 hrs. 
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Matrix

Quote from: russ_drinkwater on November 26, 2017, 02:51:35 PM
I have not read my trojan info for a while, but isn't the charge rate of 20-40% of
rated amps the go?


I have not ever seen a charge rate spec of 20-40% ... but it could be?
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Matrix

Here is my charge cycle over the course of about 4 hours. 
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

mike90045

Quote from: Matrix on November 26, 2017, 08:39:46 PM
Quote from: Westbranch on November 26, 2017, 01:47:40 PM
Matrix, how long does the unit deliver the >90Amps? Does it not decrease over time?
It does 90 + in the bulk stage for about 1.5 hrs.  Then yes, it tappers in absorb down from 90+ to 7.5 amps over 2.5 hrs.

Man, you are running your batteries down way too low, for them to be charging that hard.  If they are not getting warm, you are likely OK, but if they are getting hot, you are killing them.

Quickly running the math backwards, you are putting in about 150Ah, so if you are only discharging 20% daily, your battery bank is about 650ah ?? 

At least the charge tapers way down, and that means the batteries are still healthy.
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

CDN-VT

Same screen as type of charge with the System Control Panel (SCP) under advance
Scroll down to rate & amount of charge  .

It's worded wrong !
Cnglish  manual , hence why the tech support is bad.

VT
Canadian Solar 350W 37.6 VOC  30.6 VMP 8.22 ISC 7.87 IMP ,-15 c +30c max  4 strings in 2 in Series for 24v Classic 150 -1020 Ah  Freezers & fridges ~~~ Second Array same panels of 3sx3 parallel for 24 V Classic 150 -440 Ah Outback Barns & out blds.
48Vdc almost done,11Strings up of 3s11P same panels

Matrix

Quote from: mike90045 on November 26, 2017, 09:13:29 PM
Man, you are running your batteries down way too low, for them to be charging that hard.  If they are not getting warm, you are likely OK, but if they are getting hot, you are killing them.

Quickly running the math backwards, you are putting in about 150Ah, so if you are only discharging 20% daily, your battery bank is about 650ah ?? 

At least the charge tapers way down, and that means the batteries are still healthy.
I have 4 Trojan L16H-ACs that are in series and have 435ah.  When charging I have never seen the temp get higher than 90*F.  For the graph above the highest the temp ever got was 88*F

Here is what we have today (and this is my typical amount of daily depth of discharge):
- SOC measured by both the Whiz Bang Jr and SW Battery monitor: 68% SOC
- SOC measured by SG average all 12 cells: 1.221 which according to Trojan is just about 72% SOC (1.217 = 70%)
- Battery Temp: 76F using SW sensor on post / 67F using CC sensor on side in between batteries (out side air temp is 51F)
- Amp Hours used 139ah (according to SW battery monitor)

I only use the SW for charging every so often (like when there has been no sun).  So over 40 days of use since I started new with these batteries,  I have only every used the SW at its 90+ charge amps about 8 times at most. Most of the time I charge via the solar CC which never goes above 60 amps.

But I did figure out why the charge amps was running so hi when charging from the Conext SW 4024.  (see next post)


Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily