Magnum inverter & GFCI / AFCI
« on: July 11, 2018, 07:58:04 PM »
My curiosity about this inverter is killing me. I can test once the batteries arrive but I haven't heard a shipping date yet and I ordered them 2.5 weeks ago.

The manual for the MagnaSine PAE4448 inverter includes a warning:

Quote
2.3.3 Recommended Ground Fault Circuit Interruption (GFCI) Breakers
In compliance with UL standards, Sensata has tested some GFCIs to ensure they function properly
when connected to the inverter’s AC output. See WARNING below.

WARNING: Risk of electric shock. Use only the following GFCIs [receptacle(s) or circuit
breaker(s)]: Leviton #8899-A, N7899, GFNT1 and GNNT2. Other types may fail to
operate properly when connected to this inverter.

NEC now requires GFCI plus AFCI for circuits to most rooms of a residence and none of the listed devices provides AF protection.  Magnum tech support suggested that the problem was nuisance trips or failure to reset.

I can find only a single online mention of nuisance trips with a Magnum and it was really an oversensitive GFCI device. (On AW&S forum.)

Has anyone had trouble with GFCI breakers or outlets connected to a Magnum split-phase inverter? Experience with combined GFCI / AFCI breakers or outlets? The main panel at the new place is Square D plug-on-neutral and I wanted all GFCI and AFCI in the panel so if the first outlet in a circuit ends up behind furniture resetting would not mean moving furniture. I have a single AFCI / GFCI breaker to test once the batteries arrive.

Is this a real problem?

Thanks for any help.
« Last Edit: July 11, 2018, 08:00:36 PM by DEinME »
4800W PV in 2 circuits of 96V & 50A each after the Midnight combiner. Two Midnight Classic 200. MagnaSine 4448 split phase inverter on a Midnight e-panel. 700Ah or 900Ah FLA @ 48V. Birdhouse,WBjr, etc. Replaces 16-year-old off-grid full-time 408W PV & 300W Morningstar inverter.

Robin

  • Hero Member
  • *****
  • Posts: 541
Re: Magnum inverter & GFCI / AFCI
« Reply #1 on: July 11, 2018, 08:54:25 PM »
UL requires manufacturers to test GFCI devices and list them in the manual. If they didn't test one, they have to say there may be a problem. This is a throw back from modified sinewave days. I seriously doubt there are any problems with any modern sinewave inverters.
Robin Gudgel

DEinME

  • Newby
  • *
  • Posts: 20
Re: Magnum inverter & GFCI / AFCI
« Reply #2 on: July 12, 2018, 04:59:07 AM »
Thank you, thank you, thank you.
4800W PV in 2 circuits of 96V & 50A each after the Midnight combiner. Two Midnight Classic 200. MagnaSine 4448 split phase inverter on a Midnight e-panel. 700Ah or 900Ah FLA @ 48V. Birdhouse,WBjr, etc. Replaces 16-year-old off-grid full-time 408W PV & 300W Morningstar inverter.

DEinME

  • Newby
  • *
  • Posts: 20
Re: Magnum inverter & GFCI / AFCI
« Reply #3 on: August 23, 2018, 05:13:57 PM »
UL requires manufacturers to test GFCI devices and list them in the manual. If they didn't test one, they have to say there may be a problem. This is a throw back from modified sinewave days. I seriously doubt there are any problems with any modern sinewave inverters.
As you predicted there is no problem.

It's been a couple weeks and I've installed both 15A and 20A breakers. They're all Square-D Homeline Plug-on-neutral breakers. And they work just fine.

I wonder why Magnum tech support couldn't have explained that it's a required warning and not necessarily a problem

Again, thanks.
4800W PV in 2 circuits of 96V & 50A each after the Midnight combiner. Two Midnight Classic 200. MagnaSine 4448 split phase inverter on a Midnight e-panel. 700Ah or 900Ah FLA @ 48V. Birdhouse,WBjr, etc. Replaces 16-year-old off-grid full-time 408W PV & 300W Morningstar inverter.

boB

  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2764
Re: Magnum inverter & GFCI / AFCI
« Reply #4 on: August 23, 2018, 08:55:48 PM »

I wonder why Magnum tech support couldn't have explained that it's a required warning and not necessarily a problem

Again, thanks.

Most likely because some of the old-timers probably remember but the new timers may not have been asked or entitled with that bit of old knowledge.

You may or may not get an old wise one when you call Magnum.  I bet that Tony Boatwright there would remember.

boB