Breaker compatability question

Started by WillEert, July 25, 2018, 08:47:34 PM

Previous topic - Next topic

WillEert

Can one put a MNDC-GFP50-300 in the MNPV6-Disco? I am sure one can but I can't find the GFP on the breaker compatibility list and I don't want to buy this equipment and then find out it does not work.

I asked this question elsewhere but no reply and I would like to get the equipment ordered.

Thanks

Will
(1)24 ET 185 mono, Classic 150,8x Surrette 6CS25p, 4x Magnum 4448, homecooked diversion system;(2)15 Heliene 330 mono,Classic 150;(3)2X6 Hansol345mono, 2 stand alone Hotspot ACDC12C Minisplit heat pumps.(4)15 Hanwha Q cell 400 1/2 cell, Classic 200: (5)1X6 HanwhaQcell 400 1 Hotspot minisplit ACDC18C

FNG

Will,
yes any of the din rail breakers that are DC or the black bodied AC are exactly the same form factor. So that said yes that GFP50-300 will fit and use 4 of the 6 breaker locations