Author Topic: Breaker compatability question  (Read 162 times)

WillEert

  • Full Member
  • ***
  • Posts: 156
Breaker compatability question
« on: July 25, 2018, 08:47:34 PM »
Can one put a MNDC-GFP50-300 in the MNPV6-Disco? I am sure one can but I can't find the GFP on the breaker compatibility list and I don't want to buy this equipment and then find out it does not work.

I asked this question elsewhere but no reply and I would like to get the equipment ordered.

Thanks

Will
(1) 24 ET 185 mono, Classic 150,8x Surrette 6CS25p, 3x Magnum 4448, homecooked diversion system;
(2) 15 Heliene 330 mono, Classic 150; (3) 2 X 6 Hansol 345 mono, 2 stand alone Hotspot ACDC12C Mini-split heat pumps.

FNG

  • Administrator
  • Jr. Member
  • *****
  • Posts: 85
Re: Breaker compatability question
« Reply #1 on: July 26, 2018, 08:51:34 AM »
Will,
yes any of the din rail breakers that are DC or the black bodied AC are exactly the same form factor. So that said yes that GFP50-300 will fit and use 4 of the 6 breaker locations

WillEert

  • Full Member
  • ***
  • Posts: 156
Re: Breaker compatability question
« Reply #2 on: July 26, 2018, 09:28:33 AM »
Thank You!!!!

Will
(1) 24 ET 185 mono, Classic 150,8x Surrette 6CS25p, 3x Magnum 4448, homecooked diversion system;
(2) 15 Heliene 330 mono, Classic 150; (3) 2 X 6 Hansol 345 mono, 2 stand alone Hotspot ACDC12C Mini-split heat pumps.