Author Topic: KIDD won't charge after storm  (Read 349 times)

Vic

  • Hero Member
  • *****
  • Posts: 2028
Re: KIDD won't charge after storm
« Reply #15 on: September 10, 2018, 03:35:02 PM »
Hi again jrodr...,

Should have added,   that you might try a different charge Mode in the KID:

Try setting the Legacy O&P  Mode,  to see if that increases the amount of output current you see.

Please let us know how you are doing,   Thanks,   Vic
Off Grid - Two systems -- 4 SW+ 5548s, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 3X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  Thanks MN for Great Products/Service/Support!

jrodrigz99

  • Newby
  • *
  • Posts: 4
Re: KIDD won't charge after storm
« Reply #16 on: October 16, 2018, 04:55:08 PM »
Sorry for being so late with the update. Just a couple minutes ago I wired 6 new 255 W panels to the Kid (2 strings of 3 modules each) and it is working nice, even better than the Schneider. So, will wait a couple days for battery to recover and then equalize. What happened with the Kyoceras was that some panels developed what it seems to be a web of cracks or delamination, I am not sure, and voltage was right but amps were very, very low. Talked to a Kyocera representative and told me to take apart the panels that did not show any sign of problems and wire them to my system. I did, but panels behaved as bad as the one with webs, so, I am going to test each individually with a Morningstar PS-30 charge controller and a 12V battery and going to order some diodes for further testings if needed.

Thanks to all of you who gave me recommendations.
« Last Edit: October 16, 2018, 05:01:06 PM by jrodrigz99 »

ClassicCrazy

  • Hero Member
  • *****
  • Posts: 1901
Re: KIDD won't charge after storm
« Reply #17 on: October 16, 2018, 07:06:46 PM »
you can take the two wires from  each individual panel  and short them together and get the Isc short circuit current. You either have to have a DC capable clamp amp meter or use a regular DMM amp meter in series in the amp setting.

Larry
system one
Classic 150 , 5s4p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system two
Classic 150 ,5s 135 watt Kyocero , 16s Calb 100AH LiFePO4 , Outback VFX 3648 inverter
system three
Midnite KID MPPT 24 DC in to  12 volt AGM batterie