Recharging BB by generator and charger?

Started by sigp2101, November 19, 2018, 01:24:55 PM

Previous topic - Next topic

sigp2101

Hi all,

Every time prior to topping up my BB with generator I disconnect all of the other components of the system fearing that if I do not do that may inflict some damage to controller or inverter.

Am I being silly.?
Off grid system:
3 X 230W 36V 8A SolarWorld in series,
Classic 150,
36V BB - 225Ah 6x6V Trojan T-105 T2,
3000W psw Inverter,
Fridge 159KWh/Y, 30W led lights, laptop, TV.

Westbranch

#1
Not if you want to make sure all the generator power goes into the BB, otherwise no need to disconnect.

What  charger are you using ? How often? Do  you EQ?

A WBjr on the system would be useful so you can see exactly how many Ahr's go into the bank
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

sigp2101

#2
Oh, the charger is 36V 25A golf cart charger.
https://www.amazon.ca/Schumacher-INC-3625A-Amp-Digital-Charger/dp/B009PHKSDI

No settings on it. It stops charging when it thinks system is full. No EQ options on it.
Off grid system:
3 X 230W 36V 8A SolarWorld in series,
Classic 150,
36V BB - 225Ah 6x6V Trojan T-105 T2,
3000W psw Inverter,
Fridge 159KWh/Y, 30W led lights, laptop, TV.

tecnodave

Sigp2101,

This type of charger does not have any voltage controls incorporated and cannot regulate voltage.
I would suggest running the charger without the loads first to discover the maximum voltage this charger delivers. Normally golf carts are charged when no Equiptment is on so no matter if voltage too high.

I would recommend a proper 3 or 4 stage charger for those batteries. They will live a lot longer, maybe twice as long.

David
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P