Follow-me... do you have end amps and absorb time programmed into yours?

Started by alyaz, February 04, 2019, 09:59:15 PM

Previous topic - Next topic

alyaz

First few sunny days happening here, so just trying to make sense of my newly set up Classics that are in ‘follow-me mode.’

The master gets to end amps (all three have end amps of 12a programmed into them and all three have absorb time of 6 hours also set) and starts the float timer.  The other two, seem to just continue on in absorb for the six hours...  Today for example the Master shows about 30 minutes in float, the other two show about 5 1/2 hrs in absorb. 

The tech from Midnite helped me set them up and said they would either get to end amps and go into float or if end amps wasn’t met, then they would default to the set absorb time.

This is not what I imagined happening...  I thought all three would go into float once the master read the end amp setting from the attached WBJr shunt (all three Classics do have the ’shunt’ option engaged)...  all three Classics are showing the blinking blue light that suggests they are communicating properly..

Should I adjust the set default time?  Or does this seem normal?
3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

tecnodave

Alayz,




I think you have a setting wrong........"all three classics have shunt set"........ I'm pretty sure that would be set only on the one reading the shunt.  If the others have that set then they won't know to det that data from the one having the shunt.

Bet that one that went to float has the shunt and the others could not read that shunt and did not see end amps meet desired value.

David
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P

ClassicCrazy

From Midnite Knowledge base
http://www.midnitehelp.com/


CLASSIC - F-ME - How to setup Classics in true Master/Slave Mode
The Follow-Me concept does not embrace Master/Slave topology.  With a few "tweaks" you can have a simple master/slave setup which I find personally works better.  Below I will tell you how it's done and explain how it works. (this may have limited benefits for 2 Classics)

First, we need to pick a Classic to be our Master Controller.  It will be called the "BTS MASTER"  Why is this?  Because one of the neat advantages of having F-Me setup is we can use a single BTS (Battery Temperature Sensor) and not need 2 or 3 or 4 or xx sensors and all that extra wire tied up somewhere.  The BTS-NET option in the Classic allows a single BTS to provide data to all Classics.  The BTS-NET is also a easy way to check that the cables are good and the F-Me network is functional.

1 - Pick a BTS MASTER Classic, install the BTS and set it to MASTER in the TWEAKS MENU under BTS-NET (page down to get to the sub-menu)
All other Classics get this set to FOLLOW.  This should be self explanatory to most seasoned Solar Installers & Electricians.

2 - If the Whizbang Jr SHUNT Option is going to be installed, install it in this Classic. This Classic will be the "Master of all things". This will be required for ENDAMPS control.

3 - All charging voltages get set the same.  The only thing we set differently is CHARGE TIMES.

4 - Set your needed ABSORB TIME in the Master, the rest (Slaves) get set with that plus 10 minutes.  See, what this does it lets the Master decide when to send everyone to Float.  If for some reason F-Me breaks, all that happens is the slaves stay in Absorb for an extra 10 minutes.

A GF or Ground Fault seems to only shut down the offending Classic so we should not need to worry about down-stream Classics sending data back around. AF or Arc Fault seems to exhibit the same behavior, at least on my 5 Classic system.

There is a misconception that ABSORB is a F-me function, it is not.  ALL Classics MUST reach their Absorb voltage independently.  ANY Classic that fails to maintain the programmed Absorb Voltage for 90 seconds with be forced BACK into BULK and this mode will be propagated around the F-Me network forcing all Classics back into Bulk.

If using ENDAMPS and REBULK set it up ONLY in the MASTER, let it decide since it has the WhizbangJR (Needed for proper ENDAMPS Operation)  Don't use ENDAMPS unless you have a WBjr installed & setup to use the SHUNT.

I have removed the Follow-Me cable from the LAST Classic to the FIRST on my system.  Everything goes ONE-WAY from the MASTER on the LEFT to the others on the RIGHT or Down-Stream.  This seems to be working, this stops the "SLAVES" from sending modes back to the MASTER flipping it.  I like it better but it is not a Midnite supported mode of operation. I like the MASTER to be in total control.

Hope this helps, Jim Parish

Help Topics:

Last updated Wed, Aug 9 2017 12:58pm
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

ClassicCrazy

Master Classic has ending amps set in follow me. the slave has 0 set for end amps since that disables it.
Since the slave follows the master once the master is satisfied on end amps it goes to float and the others follow it.
You may notice different charging amps from each classic - they don't always contribute the same amount since they are independent that way. I have my classics all going through the same shunt for the master, though I also have whizbang and shunt on the slave. The master system amps  on my system shows the combined output from both - the slave only shows it's output .

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

alyaz

3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

alyaz

Have tried everything and no change.  I am thinking the phone cords I bought online through ‘The Source’ are not right. 

The blue light flashes are not 1/10th of a second, but probably more like 1/2 second long.  So, I am guessing that the Classics are not communicating.

Sometimes living remotely in Canada really sucks.  Will try to order cables directly from Midnite this time...

Is anyone aware of a video that shows the flashing blue light in a Classic -  when correctly connected and communicating?
3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

Westbranch

look at these ...  I believe there is on with Ryan(?) showing the flashing LEDs opn one that I remember  http://www.midnitesolar.com/videoDisplay.php
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

alyaz

Thanks Westbranch.  I have seen the ones associated to the follow-me mode and the webinar they did on the follow me too.  I couldn’t pick up the flashing blue lights in any of them.  No worries.  I have MN cables coming - hopefully I will have them within a month.  Then will give that a try.
3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

ClassicCrazy

They are just regular 4 conductor telephone cables .  I had a long one and chopped it in two and then put ends on - but did them wrong at first because I thought they would be the same on both ends but actually sort of look opposite - even though the wires go to the same pins at each end . Not sure I am explaining that right but regular 4 conductor telephone cables are what they are.

Too bad you are having that trouble - Did you ever get any of the follow me working at all ? You couldn't see the same temperature in each when you set the one to master ?

Maybe if you write down the settings for Follow me for each Classic  and compare them you can spot if something is not right - or share them with us and we can see if they look right. 

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

alyaz

Thanks ClassicCrazy.

I have been through the settings three times now with the very patient Louis (tech). 

I am guessing that because these phone cables are from ’The Source’ that something isn’t right with them, but who knows.

I just read another forum post on how to check the cables.  (On each Classic run the cable from the middle port to the bottom port and should see a quick flashing blue light - if the cable and Classic are operating correctly).  I will try that tomorrow.

My flashing blue lights seem to be a half second long.  So I am guessing that the cords are the issue as it is odd that all three Classics are blinking the same length of time.  Which all seem to be slower than 1/10th of a second.

Can the Classics be left powered up when removing and plugging the phone cords in?

Thanks.
3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

ClassicCrazy

I left the Classics on when I plugged them in and out .
If you have a multimeter you can ohm out the cables to see if they have continuity on each pin.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

alyaz

3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

alyaz

So, couldn’t wait till morning, cause this was bugging me.  So I went down and popped the covers off of the Classics, and checked each phone cord between the middle phone input and the bottom input and none of the phone cords I had purchased online from ‘The Source’ checked out.   :-\ 

I had two little MNGP shorty cable spares and one long old phone cord.  Popped them in and I now have a short burst of blue light on each Classic and the temperatures all display as per the Master’s BTS (which wasn’t displayed before).

I can’t close the Classic covers properly for now so will await the MN phone cables before I button them back up properly.

You know, I couldn’t find reasonably short phone cables up here, so I went online and found that ’The Source’ had ten footers.  I called and confirmed they were RJ11 / 4 pin regular phone cables.  I was assured they were so purchased them.  ’The Source’ is like the Walmart of electronics up here in Canada.  So very frustrating.

Thanks for all the help.  Seems that is all it was.

A couple of things that were extremely valuable, learned here from you guys:
1. How to easily check the cables by running them between the middle and bottom phone input jacks on the Classic;
2. The short blue light burst versus the longer blue light burst.  I took for granted that the short blip I was seeing was okay when in fact it was a sign (to the experienced eye) that there was no communication occurring.  Kinda too bad that wasn’t more obvious, but now I know.

Gawd.  Going to go colour my grey hair now and start drinking again  ;)

3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

ClassicCrazy

good to hear you figured out the problem.
Strange that those phone cords don't work .  Maybe take a good look at them and see if the wires cross from one connector to the other instead of being straight through.  Not sure why they would be that way but sounds like there is some problem with them.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

alyaz

Hi Larry.

I will probably look at them closer tomorrow, right now I never want to see them again   >:(

I will be talking to ‘The Source’ tomorrow morning though.  Ha.

Thanks again.
3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.