New System Design Help Needed

Started by Beyla, February 18, 2019, 01:03:39 PM

Previous topic - Next topic

Beyla

Hi and thanks for looking into my request for help.

I have a Classic 150, Magna MS4024, MNPV6 Combiner, and an 8 X 6volt battery bank configured for 24 volt. My MNPV6 Combiner is on the outside wall at eye level and approximately 4 feet from the solar array. I plan to have 6 strings of 2 panels going to @15Amp breakers in the MNPV6 combiner. I could also got with 4 strings of 3 panels and us 4X15@mps and a 63 amp breaker for output to disconnect.  I require an ESSA inspection approval and that means a disconnect on the outside wall for the solar DC incoming from the roof, they won’t accept disconnecting by swinging open the MNPV6 cover and shutting the 6 breakers off t disconnect the solar array. I could position a Disconnect with a red pull down level on its side below the combiner and then feed the positive and negative from the output of the combiner to the disconnect and then to the inside. I think I will require the e-panel 250Amp to facilitate and comply with the installation. I would appreciate any help you can provide me with putting together this design and have it comply with the solar safety code. I have all the wires and proper metallic electrical conduits. My distances are short since the panels are directly above and farthest solar panel to combiner PVC cable is at most 18 feet away and closest is 4 feet. Thank you to anyone who provides input.

Regards,
Classic 150, DiscoCombiner4X 6 circuit(MNPV6HV 4X), 10 panels @ 2600 Watts, MS4024 Inverter, 8XCrown 6 volt batteries in 24Vbank. Epanel 250Amps/ w remote breaker and Birdhouse.WhizBang Jr., BTS.

mike90045

I'd put the DC disco after the combiner.    Will they let you use a breaker, or do they want a box with a handle outside?
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Beyla

Here is a link to their requirement, it’s a little obscure and some companies have said I need the red handle but my combiner is so close to the array and on he wall with 6 breakers that can cut the power.

https://www.esasafe.com/assets/files/esasafe/pdf/Bulletins/64-6-0.pdf

Regards and thanks,
Classic 150, DiscoCombiner4X 6 circuit(MNPV6HV 4X), 10 panels @ 2600 Watts, MS4024 Inverter, 8XCrown 6 volt batteries in 24Vbank. Epanel 250Amps/ w remote breaker and Birdhouse.WhizBang Jr., BTS.

Wizbandit

The MNPV6 Breaker combiner box has a version with a red handle on it to turn off all 6 breakers from the front, did you know?

Quote from: Beyla on February 18, 2019, 06:03:01 PM
Here is a link to their requirement, it’s a little obscure and some companies have said I need the red handle but my combiner is so close to the array and on he wall with 6 breakers that can cut the power.

https://www.esasafe.com/assets/files/esasafe/pdf/Bulletins/64-6-0.pdf

Regards and thanks,

Beyla

No, they won’t accept that because it’s a two step process, I know, kinda ridiculous, but they have their ridiculous reasons, so I can’t use that kit. I would still prefer to get the certified disco-combiner with birdhouse, not an issue for that, thanks for your input, much appreciated.
Classic 150, DiscoCombiner4X 6 circuit(MNPV6HV 4X), 10 panels @ 2600 Watts, MS4024 Inverter, 8XCrown 6 volt batteries in 24Vbank. Epanel 250Amps/ w remote breaker and Birdhouse.WhizBang Jr., BTS.

Westbranch

Beyla, what province are you in?  I don't like the sounds of this ' don't like the 2 step process' stipulation...
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Beyla

Ontario.
Thanks.

I got the DiscoCombiner 4X with 6 circuits and the red arm along with the PSB that connects it to the birdhouse, along with the epanel but not the -RSS panel, so I had to buy a Remote Trip Breaker @250 Amps and a Battery Disco board. I posted a new thread for help on how to wire these two components into my STMN250 epanel.
Classic 150, DiscoCombiner4X 6 circuit(MNPV6HV 4X), 10 panels @ 2600 Watts, MS4024 Inverter, 8XCrown 6 volt batteries in 24Vbank. Epanel 250Amps/ w remote breaker and Birdhouse.WhizBang Jr., BTS.