Will the MNEDC series breakers fit inside the MNDC125?

Started by qrper, August 28, 2019, 02:36:32 PM

Previous topic - Next topic

qrper

Subject line says it all.

I downloaded the manual for the DC125, and i don't see where it will support the larger bolt terminal circuit breakers such as the MNEDC80.

I found out today on a cold bright day and produced more power than the 63 A breaker in the baby mini box.

Mike
System one: 7kWp w/ Trina 250 W panels @90 Vdc. Classic 150 to 16-6 V U.S batteries. Trace 5548 sine wave inverter.
System two: 6kWp grid tie with solaredge inverter.
System three: Midnite Brat, two 120 W Astropower modules, 100 Ah battery. Runs the LED streetlight in the back yard.

Vic

Mike,

Do you have room for the MNEPV80,   or 100?   They are double-wide breakers:
https://www.solar-electric.com/midnite-solar-mnepv-150-volts-80-amps-array-breaker.html

They DO occupy two DIN Rail spaces.

And,   of course,   the cable that connects to these breakers would need to be rated for 80 (or 100) Amps.

There is an adapter that allows mounting up to three MNEDC breakers instead of DINs,   but  cannot find it as an accessory   ...   did it come with your MNDC-125?

Just a thought of two,   73  GL   Vic