AUX 2 for input

Started by binkino, October 04, 2019, 11:10:01 AM

Previous topic - Next topic

binkino

I apologize, I lost the trace ... had not really much time, much time is gone again - somewhere it was answered, but can't find it

If I want to use AUX2 for input (closing the 2 terminals of Aux2 with relay) what setting must been done?


Many thanks! ;)
PV-OUTPUT: http://pvoutput.org/list.jsp?id=38617
Classic Lite 200 + Classic 200 + Easun ISolar-SMX-II-5.6KW + 12x240Wp + 12x255Wp + 2x10kWh LFP
http://a68k.de/Solar/Monitor_LC2.php

FNG

#1
You won't find it in the Local App, We, unfortunately, have not kept that up with current production firmware.

On the MNGP you will find Logic input 2 and Logic input 1

Logic input 2 forces resting when the terminals are less than 2 volts (Shorted) and allow charging when the terminals are above 6v
Logic input 1 forces resting when the terminals are above 6 volts and resumes charging when they drop to 2v or less

My memory is a little foggy, I recall one of these states needs an external pull up or pull down resistor and the other state has it buit in. Jim from tech support had this documented and I will work to find that and post it

So logic input 2 forces resting when voltage is 2 v or less and does NOT have a pull up resistor internally, So if using a relay to close the Aux terminals for Logic input 2 you will need to provide a pull up resistor to bring the voltage on Aux2 + above 6v when the relay is open. If you need any help with that please reach out to our support dept at support@midnitesolar.com

binkino

Thanks ;)

ouh have I been so wrong now ...  that's why I can't find it ... mh... ok ;)
(I would set a bet, but ok ;) )

On the Classic I want to use the AUX2 for input, I have no MNGP, this is a "lite" Classic

PV-OUTPUT: http://pvoutput.org/list.jsp?id=38617
Classic Lite 200 + Classic 200 + Easun ISolar-SMX-II-5.6KW + 12x240Wp + 12x255Wp + 2x10kWh LFP
http://a68k.de/Solar/Monitor_LC2.php

FNG

That will be an issue as I dont see the engineers adding any features to the local app, I will ask the tech support dept what your options are

Vic

Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

binkino

Quote from: FNG on October 04, 2019, 11:49:57 AM
That will be an issue as I dont see the engineers adding any features to the local app, I will ask the tech support dept what your options are

Are there some news?

Yes, the LocalApp ... :D
Why is this treated so neglected ..... ;(

BUT there can be other ways to send settings to the Classic

Thanks to Wade, meanwhile I can change settings in my webbrowser, hidden behind my "LCARS" designed showing my PV datas.
That should be easy to add an option, for sending a setting to the Classic.
(but updating firmware again ... only if I really must haha)


Quote from: Vic on October 04, 2019, 12:08:59 PM
There is a bit of Aux 2 info here:

http://www.midniteftp.com/support/kb/faq.php?id=106

FWIW,   Vic

thanks but doen't help me here (or I don't understand)



Temporarly I added a "logic function" in the website.
Just simple.
If power use is below  70 watts, the inverter is 100% on grid.
That's not the perfect way. For the moment now, it works for me.
With this new value in memory, I hope I can go further in my ideas.