How should i set up my (3x) 48v 540Ah off grid system...

Started by The Ugly One, November 27, 2019, 01:15:22 PM

Previous topic - Next topic

The Ugly One

So i have no clue what would be the best way to set this up.
42 x - suniva 260 watt panels
3 x -douglas 48v 540ah forklift batteries.
Alot of random equipment that wont make the cut.
So that is what i am starting with. I have 3 buildings that will need 4800 watts going to each. I planned on using the batterys each night and charging them fully the following day. While still using some left over pv power that isnt charging the batteries to have some power to use also. I will be adding to my system down the line. There is nothing electrical in the hiildings and they sit side by side in a run of 6. I am trying to set up with having them working without having to redo the system down the line. I thought i would have a battery per building and a system to go with it. I can use 12 panels to charge the battery from empty to full in a 10 hr day. I am not opposed to building a power house and having everything in one area. What does the forum say with my idea?... i have the batteries and panels already what options do i have available?
I take them Ray Rays, and turn them into that Boom Boom Zap Juice.

Westbranch

First  question...  are you in the tropics or the frozen North (or South) and how many hours of sunlight will you be getting on Dec 22?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

ClassicCrazy

The deeper you cycle those batteries the less life they will have. For optimum longevity the batteries need to be not hot, and ideally only drawn down 20% except for occasionally taking them deeper for battery health ( stirring up the electrolyte and equalizing) .

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

The Ugly One

I live in the hills of Mendocino county in northern california..

I know the deep cycle batteries shouldn't be drained past 80%. But I thought I read somewhere that the 48v battery should be drained way down each day used. Then give it a full charge because they are good for over 5000 charges. And the battery doesn't k ow the diff between a top off charge or a full charge.


I take them Ray Rays, and turn them into that Boom Boom Zap Juice.

mike90045

#4
here's my observation -

Batteries will only cycle so many watt hours thru them.   

You can accomplish that with 2 years of deep cycles, 4 years of moderate cycles or 8 years of shallow cycles.

I too live in Mendonesia and with this storm, I'll be burning diesel this week +

http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV