Hi guys, I've got the MNBDM mounted in my E-panel. Looking at the connection to the 250A main DC breaker, terminals on the MNBDM say + and -, but both of the wires from the breaker are yellow and appear to be connected together at the end(?). Perhaps this just a 'normally closed' situation where polarity doesn't matter but as soon as I snip the wires apart the breaker will trip, right? Or am I just confused?
SMA Solar Sunny Island SI6048
JA Solar 330W 72 cell panels (18)
Classic 250 (2)
MODBUS/Canbus comm adaptor for Sunny Island
SMA-OG E-panel
WhizBang Jr
MNSPD300V (3)
Atkinson GSCM mini-i
Onan Quiet Diesel QD-8000
200Ah (soon 600) Aolithium LiFePo4 51.2v
Off the grid on the PNW coast

FNG

The MNEDC175RT and MNDC250RT breakers have the trip coil, This coil is not polarity sensitive so the + or - from the BDM can go to yellow wires and you don't have to worry about polarity