As I'm studying the 2017 NEC that now applies in my county, I came across this sentence under Wiring Methods, Methods Permitted, Identification and Grouping [690.31(B)]:
"PV source circuits and PV output circuits shall not be contained in the same raceway, cable tray, cable, outlet box, junction box, or similar fitting as conductors, feeders, branch circuits of other non-PV systems, or inverter output circuits, unless the conductors of the different systems are separated by a partition."
It seems to me that the inverter output AC wiring in the E-Panel shares the same main compartment with the PV source circuits and charge controller output circuits.
This would seem to directly violate this NEC paragraph.
What am I missing here?