I have (2) 24v wind turbines to add to my current system.

It appears that I can just wire them directly, but is there a better (more efficient?) way to do this?
(Charge controller?)
Stone - (s/v Ninaa Ootakii)

8x 265w pv, 18x 216w pv
2x 24v chinook turbines
2x classic 150s
8x L-16s
8x GC2s

mike90045

  • Hero Member
  • *****
  • Posts: 841
    • The Ranch (via facebook re-direct)
Re: s/v Ninaa Ootakii - best way to utilize (2) 24v chinook wind turbines?
« Reply #1 on: October 25, 2021, 10:50:03 PM »
Wind generators generally need 2 extra things that solar power does not:

* Redundant sets of brakes

* Charge controller with a DUMP LOAD

Brakes are to shut it down when it's sick, or possibly when commanded by the charge controller

Dump Load is required to keep the turbine loaded so it does not freewheel at 18K rpm when batteries are full.
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Stone

  • Newby
  • *
  • Posts: 39
Re: s/v Ninaa Ootakii - best way to utilize (2) 24v chinook wind turbines?
« Reply #2 on: October 26, 2021, 01:13:59 AM »
*nods*
They come with diversion loads.
(these are/were a midnite solar product).

I'm going to be using hydronic heating, so dumping excess power to a hot water heater may be in the future as well, maybe.

The diversion loads are pulse width modulated, and, well, it's a midnite product, so likely "best it gets" ... but tech changes every day, so I figured I should ask :)
Stone - (s/v Ninaa Ootakii)

8x 265w pv, 18x 216w pv
2x 24v chinook turbines
2x classic 150s
8x L-16s
8x GC2s

ClassicCrazy

  • Hero Member
  • *****
  • Posts: 3040
Re: s/v Ninaa Ootakii - best way to utilize (2) 24v chinook wind turbines?
« Reply #3 on: October 26, 2021, 01:43:09 PM »
*nods*
They come with diversion loads.
(these are/were a midnite solar product).

I'm going to be using hydronic heating, so dumping excess power to a hot water heater may be in the future as well, maybe.

The diversion loads are pulse width modulated, and, well, it's a midnite product, so likely "best it gets" ... but tech changes every day, so I figured I should ask :)

Check this page for a wind generator dump controller project
https://www.windsine.org/

Larry
system one
Classic 150 , 5s4p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system two
Classic 150 ,5s 135 watt Kyocero , 16s Calb 100AH LiFePO4 , Outback VFX 3648 inverter
system three
Midnite KID MPPT 24 DC in to  12 volt AGM batterie

RicardoL

  • Newby
  • *
  • Posts: 5
Re: s/v Ninaa Ootakii - best way to utilize (2) 24v chinook wind turbines?
« Reply #4 on: November 25, 2021, 03:27:40 AM »
In addition to offering a variety of products and services, custom software developers can also cater to niche markets. Small businesses, for example, may require a simple application for internal use. But in large companies, complex systems can be designed for large enterprises. Depending on your needs and budget https://mlsdev.com/blog/54-benefits-of-outsourcing-mobile-app-development, bespoke software development is a great way to meet your specific requirements. But be prepared to pay for it if it's worth it. It's more than worth it if it's customized for your company.