Shunt Question

Started by LilMT, February 04, 2022, 10:58:08 AM

Previous topic - Next topic

LilMT

I have a MNEMS4448PAECL250 system (and I love it). 
In the winter I will not have much sun and a generator will be my primary source. 
I would like to have an automatic gen start module with it and I was wondering about wiring methodology. 
The MNEMS4448PAECL250 comes prewired with the MidNite Classic 250 prewired to the shunt. 
To add a BMK and AGS from Magnum Energy to the system, can I simply add the wires to the existing shunt or do I need to add an additional shunt. 
If I need to add an additional shunt I assume I would place it in series with the exiting shunt?

Thanks,
LilMT

I should clarify.  The shunt currently has a WizBangJr on it for the MidNite.
Thanks,
LilMT

Classic 250, 3s2p Trina Solar 405watt, 8 Renogy 200ah for 48V 400ah, Magnasine 4448 inverter.

ClassicCrazy

#1
As long as the existing shunt is between the batteries and everything else - any power going into or out of the batteries will show up on whatever monitoring program you are using that already reads the midnite whizbang shunt amps.
So on one side of  shunt there should only be one negative connection to the batteries - all other negatives will be on the other side of the shunt.
When I run my generator and charge with the Outback inverter , the amps from the generator show up on monitoring program.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

LilMT

Sounds good. 

That is what I thought but I was over at a friends house and they have an Outback system and every devices that is monitoring had its own shunt.  Wasn't certain why but the system worked so I didn't question.

Just thought I should double check.

Thanks much,
LilMT
Thanks,
LilMT

Classic 250, 3s2p Trina Solar 405watt, 8 Renogy 200ah for 48V 400ah, Magnasine 4448 inverter.

ClassicCrazy

#3
I think you can even use the same shunt for more than one monitoring device if the shunt is the right specs.
They just measure the voltage drop across the shunt.
So maybe your friends system has different values shunt - like 100 ma drop on one and 50mv drop on another ?
I think the Whizbang even came with extra hardware in case you needed to hook up something else besides whizbang to the shunt.
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter