Strange reset during the day

Started by Alain Boulet, December 26, 2012, 09:15:51 PM

Previous topic - Next topic

boB


Ross, from your stats, do you think that it could have been resetting when your batteries
were full rather than needing a good charge ?   Or, maybe when the batteries were
full AND loads were light ?

boB
K7IQ 🌛  He/She/Me

RossW

Quote from: boB on August 13, 2013, 03:26:42 AM

Ross, from your stats, do you think that it could have been resetting when your batteries
were full rather than needing a good charge ?   Or, maybe when the batteries were
full AND loads were light ?

Bob, I don't think so. The times don't fit with the batteries being full. So I've done some further analysis of the logs. The following is the date/time I detected the RESET (so some time in the previous 5 mins). The next 3 fields are the battery volts, the charging power and charge state (register 4120), followed by what the same three were immediately PRIOR to the reset...


06/Jul/2013 09:35:01 49.9V    0W Resting    Prev: 51.0V 1039W BulkMppt
06/Jul/2013 10:20:02 50.1V    0W Resting    Prev: 49.3V  431W BulkMppt
06/Jul/2013 11:10:02 55.2V 2274W BulkMppt   Prev: 51.5V 1078W BulkMppt
07/Jul/2013 10:20:02 49.8V    0W Resting    Prev: 52.5V 2719W BulkMppt
07/Jul/2013 11:25:03 50.5V    0W Resting    Prev: 51.2V 1727W BulkMppt
07/Jul/2013 13:05:00 49.2V  396W BulkMppt   Prev: 49.3V  222W BulkMppt
07/Jul/2013 13:45:01 49.2V  526W BulkMppt   Prev: 49.1V  364W BulkMppt
07/Jul/2013 14:40:01 48.7V  132W BulkMppt   Prev: 48.7V  170W BulkMppt
07/Jul/2013 15:00:00 48.8V  386W BulkMppt   Prev: 48.6V  176W BulkMppt
07/Jul/2013 16:45:02 49.3V  511W BulkMppt   Prev: 49.7V  843W BulkMppt
08/Jul/2013 08:20:02 52.5V  189W BulkMppt   Prev: 52.7V  380W BulkMppt
08/Jul/2013 10:45:02 54.0V 2710W BulkMppt   Prev: 51.5V 1714W BulkMppt
09/Jul/2013 09:10:00 51.3V 1848W BulkMppt   Prev: 51.1V 1619W BulkMppt
09/Jul/2013 09:15:01 51.6V 2095W BulkMppt   Prev: 51.3V 1848W BulkMppt
09/Jul/2013 12:35:02 50.8V  132W BulkMppt   Prev: 57.8V 2372W Absorb
09/Jul/2013 14:55:00 50.1V  419W BulkMppt   Prev: 50.9V 1002W BulkMppt
10/Jul/2013 16:55:01 50.0V  430W BulkMppt   Prev: 50.4V  466W FloatMppt
11/Jul/2013 08:55:07 48.9V    0W Resting    Prev: 49.0V  961W BulkMppt
11/Jul/2013 09:55:01 50.9V 1715W BulkMppt   Prev: 50.6V 1168W BulkMppt
11/Jul/2013 11:55:01 51.4V 1961W BulkMppt   Prev: 51.9V 2208W BulkMppt
12/Jul/2013 08:35:00 49.8V    0W Resting    Prev: 50.2V   65W BulkMppt
12/Jul/2013 08:50:02 50.8V 1359W BulkMppt   Prev: 50.8V 1285W BulkMppt
12/Jul/2013 09:10:00 50.4V  592W BulkMppt   Prev: 50.1V  724W BulkMppt
12/Jul/2013 09:15:00 50.6V  365W BulkMppt   Prev: 50.4V  592W BulkMppt
12/Jul/2013 13:25:02 50.0V  586W BulkMppt   Prev: 49.7V  449W BulkMppt
12/Jul/2013 13:45:00 52.5V 1481W BulkMppt   Prev: 50.5V 1008W BulkMppt
12/Jul/2013 13:50:00 52.7V 1870W BulkMppt   Prev: 52.5V 1481W BulkMppt
13/Jul/2013 10:25:00 51.0V 1174W BulkMppt   Prev: 50.5V 1064W BulkMppt
13/Jul/2013 10:30:00 53.7V 2570W BulkMppt   Prev: 51.0V 1174W BulkMppt
13/Jul/2013 10:35:00 51.8V 1466W BulkMppt   Prev: 53.7V 2570W BulkMppt
13/Jul/2013 13:10:02 49.6V  283W BulkMppt   Prev: 49.5V  253W BulkMppt
13/Jul/2013 13:30:01 50.0V  662W BulkMppt   Prev: 50.0V  522W BulkMppt
14/Jul/2013 13:25:02 47.8V    0W Resting    Prev: 47.9V  182W BulkMppt
14/Jul/2013 15:55:01 51.7V    0W Resting    Prev: 51.8V   51W BulkMppt
15/Jul/2013 12:35:00 48.8V  116W BulkMppt   Prev: 48.8V  102W BulkMppt
16/Jul/2013 12:10:00 49.8V  989W BulkMppt   Prev: 50.2V  975W BulkMppt
16/Jul/2013 13:50:00 48.7V    0W Resting    Prev: 48.3V   24W BulkMppt
16/Jul/2013 15:00:01 48.7V  248W BulkMppt   Prev: 48.5V   92W BulkMppt
16/Jul/2013 16:35:02 48.1V   53W BulkMppt   Prev: 48.2V   72W BulkMppt
17/Jul/2013 09:05:00 49.9V  331W BulkMppt   Prev: 50.6V 1041W BulkMppt
17/Jul/2013 09:10:01 49.7V  289W BulkMppt   Prev: 49.9V  331W BulkMppt
17/Jul/2013 15:40:00 48.4V   43W BulkMppt   Prev: 48.6V  175W BulkMppt
17/Jul/2013 16:25:02 48.1V   48W BulkMppt   Prev: 48.2V   57W BulkMppt
18/Jul/2013 08:05:01 56.4V  490W BulkMppt   Prev: 53.9V   37W BulkMppt
18/Jul/2013 09:00:01 49.4V    0W Resting    Prev: 50.1V  412W BulkMppt
18/Jul/2013 11:25:02 57.6V 1954W Absorb     Prev: 57.7V 1980W Absorb
18/Jul/2013 13:15:00 49.9V  517W BulkMppt   Prev: 49.9V  444W BulkMppt
18/Jul/2013 13:20:01 50.7V 1463W BulkMppt   Prev: 49.9V  517W BulkMppt
18/Jul/2013 15:20:02 49.7V  318W BulkMppt   Prev: 50.1V  516W BulkMppt
19/Jul/2013 09:45:02 49.4V  372W BulkMppt   Prev: 49.9V  350W BulkMppt
19/Jul/2013 10:25:00 50.0V  516W BulkMppt   Prev: 50.4V  499W BulkMppt
19/Jul/2013 10:40:00 50.2V  549W BulkMppt   Prev: 50.0V  542W BulkMppt
19/Jul/2013 12:25:00 50.7V  651W BulkMppt   Prev: 51.2V  194W BulkMppt
19/Jul/2013 14:05:00 49.9V      0W Resting     Prev: 50.6V  641W BulkMppt
19/Jul/2013 15:00:01 49.0V  226W BulkMppt   Prev: 49.1V  177W BulkMppt
20/Jul/2013 11:15:01 57.6V 2570W Absorb     Prev: 50.3V  342W BulkMppt
20/Jul/2013 15:20:00 49.2V  437W BulkMppt   Prev: 49.2V  113W BulkMppt
22/Jul/2013 11:35:00 51.9V  167W BulkMppt   Prev: 52.5V   94W BulkMppt
3600W on 6 tracking arrays.
7200W on 2 fixed array.
Midnite Classic 150
Outback Flexmax FM80
16 x LiFePO4 600AH cells
16 x LiFePO4 300AH cells
Selectronics SP-PRO 481 5kW inverter
Fronius 6kW AC coupled inverter
Home-brew 4-cyl propane powered 14kVa genset
2kW wind turbine

robertd

i have to chip in here because I am having the same issue  I posted earlier that the machine goes into resting
/tracking but what it seems to be is that the kw/h keep resetting.  today I had poor sunshine and was at 5kw/h
at 12 o clock  and when I got home I was at 1.8kw/h
  I do monitor my system from work using software that came with classic

Wxboy

Quote from: boB on August 13, 2013, 12:55:37 AM
Quote from: Wxboy on August 12, 2013, 07:58:44 PM
Confirmed 1370 4/8.

OK, that's new enough.  Have you seen it do this since then ?

How often has it reset during the day that you know of ?

boB

It has not reset again since my post and this was the first time I've noticed it reset in months. 
Midnite Classic 150, 765 watt array, Outback Radian GS4048A inverter, 200ah 48v agm battery bank

boB

Quote from: robertd on August 13, 2013, 09:38:29 PM
i have to chip in here because I am having the same issue  I posted earlier that the machine goes into resting
/tracking but what it seems to be is that the kw/h keep resetting.  today I had poor sunshine and was at 5kw/h
at 12 o clock  and when I got home I was at 1.8kw/h
  I do monitor my system from work using software that came with classic

When the Classic reset, were the batteries full  or close to being full ??

boB
K7IQ 🌛  He/She/Me

Onlooker

Thought I would add my observations:

Just got my Midnite Classic 150 Lite installed a few days ago. It had a couple of resets yesterday in "Solar" mode, mid-day I switched to Legacy and today I've had at least 4(nice sunny day).  I am static IP, and watching with the local app, and mymidnite. The "Daily values" KWh collected so far gets set to zero after the reset. I get "The Connection was Closed" & disconnected from the Local App and am able to instantly re-open it.
My "Lifetime values" do not seem to be updating properly as well.

Using MyMidnite.com "Energy" graph, I can see the resets in that "Energy Collected" will gradually go up, then you see 'mid-day' it go down to 0 and start going up again.

No firmware updates from 1181 it came with, though it seems those here who have updated are still having the resets, perhaps wait until the next-one which I would hope will resolve the issue?


later.






boB


Again, I must ask, are your batteries full at all during the day when you see these resets ?

boB
K7IQ 🌛  He/She/Me

Onlooker

Quote from: boB on August 19, 2013, 05:41:25 PM

Again, I must ask, are your batteries full at all during the day when you see these resets ?


For me, it resets all through the day(12.2V) on the way up to and including absorb(14.4) and float(13.3).
Had a few more resets today...

After a reset it forgets it was ever in/finished absorb and trys putting it in absorb for X hours/mins before going to float again.. So I force float manually in config.
Having the "Lite" I just have the first 2 jumpers set to custom, and configure Static IP and most everything else from Local App.
The first couple days I ran it stock(jumpered) 12v, dynamic IP etc, I only noticed it reset once, I suppose I should put it back and see how much more stable it is there.

boB

Quote from: Onlooker on August 20, 2013, 01:16:49 PM
Quote from: boB on August 19, 2013, 05:41:25 PM

Again, I must ask, are your batteries full at all during the day when you see these resets ?


For me, it resets all through the day(12.2V) on the way up to and including absorb(14.4) and float(13.3).
Had a few more resets today...

After a reset it forgets it was ever in/finished absorb and trys putting it in absorb for X hours/mins before going to float again.. So I force float manually in config.
Having the "Lite" I just have the first 2 jumpers set to custom, and configure Static IP and most everything else from Local App.
The first couple days I ran it stock(jumpered) 12v, dynamic IP etc, I only noticed it reset once, I suppose I should put it back and see how much more stable it is there.


Dang !    OK, I was kind of hoping it was happening only when batteries were full.

I don't suppose you have ever noticed it reset while resting ?   RossW seems to see that his only resets while running.

boB
K7IQ 🌛  He/She/Me

Onlooker

Didn't touch/open "Local App" today, made no other changes... No detected resets for me today(vs 4+ each day previous couple of days).

Will have to test it a few more days, but looks like it has something to do with Local App interaction(when in custom config through local App, possibly). Static IP etc...


boB

Quote from: Onlooker on August 21, 2013, 05:26:41 PM
Didn't touch/open "Local App" today, made no other changes... No detected resets for me today(vs 4+ each day previous couple of days).

Will have to test it a few more days, but looks like it has something to do with Local App interaction(when in custom config through local App, possibly). Static IP etc...


Well, it used to be related to the local app and/or connections to the Classic over the Ethernet but I thought
we had fixed that.

Yes, please let it go another day or two and let's see if that keeps it from resetting.

Thank you for doing that !

boB
K7IQ 🌛  He/She/Me

RossW

Bob, please feel free to move this elsewhere if its more appropriate.

Tom (and at least one other forum member that I know of) has been having an issue where the classic communications just "stops". The classic still responds to ICMP echo-request (ping) packets, and is "listening" in as much as you can attempt to connect via TCP on the modbus port (502), however the classic refuses connections. When this happens, it appears the only way to recover is to reboot the classic.

It's been getting quite annoying for some.
Well, today I logged in on one of Tom's rPi's and wrote some simple code. (If anyone else wants to try this, let me know and I'll post it here). Basically, I set off a tcpdump which constantly monitored communications to/from one classic. A circular buffer holds the last couple of hundred lines of output. When this condition is detected (identified by the logging stopping), I write out the buffer to see what happened immediately before. (This is so I don't go wearing out his flash memory!)

Caught one just now.

It looks like everything was completely normal right up to the connection close, but the following attempt to connect failed. So I don't think it's my newmodbus - but happened after this reading and before the next.
Have the full packet contents if you want it, but here's the end of the last working poll and the start of the next.

192.168.2.88 is the rpi, .129 is the classic.


22:33:02.474832 b8:27:eb:32:ef:5f > 06:1f:d0:00:08:8f, ethertype IPv4 (0x0800), length 66: 192.168.2.88.40784 > 192.168.2.129.502: Flags [P.], seq 73:85, ack 459, win 14600, length 12

22:33:02.475738 06:1f:d0:00:08:8f > b8:27:eb:32:ef:5f, ethertype IPv4 (0x0800), length 163: 192.168.2.129.502 > 192.168.2.88.40784: Flags [P.], seq 459:568, ack 85, win 546, length 109

22:33:02.477794 b8:27:eb:32:ef:5f > 06:1f:d0:00:08:8f, ethertype IPv4 (0x0800), length 54: 192.168.2.88.40784 > 192.168.2.129.502: Flags [F.], seq 85, ack 568, win 14600, length 0

22:33:02.478527 06:1f:d0:00:08:8f > b8:27:eb:32:ef:5f, ethertype IPv4 (0x0800), length 60: 192.168.2.129.502 > 192.168.2.88.40784: Flags [F.], seq 568, ack 86, win 546, length 0

22:33:02.478660 b8:27:eb:32:ef:5f > 06:1f:d0:00:08:8f, ethertype IPv4 (0x0800), length 54: 192.168.2.88.40784 > 192.168.2.129.502: Flags [.], ack 569, win 14600, length 0

22:33:44.169613 06:1f:d0:00:08:8f > ff:ff:ff:ff:ff:ff, ethertype IPv4 (0x0800), length 60: 192.168.2.129.14177 > 255.255.255.255.4626: UDP, length 6

22:33:53.675032 06:1f:d0:00:08:8f > ff:ff:ff:ff:ff:ff, ethertype IPv4 (0x0800), length 60: 192.168.2.129.14178 > 255.255.255.255.4626: UDP, length 6

22:34:01.980791 b8:27:eb:32:ef:5f > 06:1f:d0:00:08:8f, ethertype IPv4 (0x0800), length 74: 192.168.2.88.40795 > 192.168.2.129.502: Flags [S], seq 897832033, win 14600, options [mss 1460,sackOK,TS val 75025465 ecr 0,nop,wscale 6], length 0

22:34:01.981958 06:1f:d0:00:08:8f > ff:ff:ff:ff:ff:ff, ethertype ARP (0x0806), length 60: Request who-has 192.168.2.88 tell 192.168.2.129, length 46

22:34:01.982043 b8:27:eb:32:ef:5f > 06:1f:d0:00:08:8f, ethertype ARP (0x0806), length 42: Reply 192.168.2.88 is-at b8:27:eb:32:ef:5f, length 28

22:34:02.981658 b8:27:eb:32:ef:5f > 06:1f:d0:00:08:8f, ethertype IPv4 (0x0800), length 74: 192.168.2.88.40795 > 192.168.2.129.502: Flags [S], seq 897832033, win 14600, options [mss 1460,sackOK,TS val 75025566 ecr 0,nop,wscale 6], length 0

22:34:02.982370 06:1f:d0:00:08:8f > b8:27:eb:32:ef:5f, ethertype IPv4 (0x0800), length 60: 192.168.2.129.502 > 192.168.2.88.40795: Flags [.], ack 897832034, win 546, length 0

22:34:03.680484 06:1f:d0:00:08:8f > b8:27:eb:32:ef:5f, ethertype IPv4 (0x0800), length 60: 192.168.2.129.502 > 192.168.2.88.40795: Flags [S.], seq 2111088, ack 897832034, win 546, options [mss 546], length 0

22:34:03.680671 b8:27:eb:32:ef:5f > 06:1f:d0:00:08:8f, ethertype IPv4 (0x0800), length 54: 192.168.2.88.40795 > 192.168.2.129.502: Flags [.], ack 1, win 14600, length 0
3600W on 6 tracking arrays.
7200W on 2 fixed array.
Midnite Classic 150
Outback Flexmax FM80
16 x LiFePO4 600AH cells
16 x LiFePO4 300AH cells
Selectronics SP-PRO 481 5kW inverter
Fronius 6kW AC coupled inverter
Home-brew 4-cyl propane powered 14kVa genset
2kW wind turbine

steve

Hi,

I am seeing similar behavior here.   I have four classic 250's running v1401. Two days ago at 1500 eastern one of them stopped talking to mymidnite.    It continued to respond to the local status panel application.   i rebooted it a few hours later and it started talking immediately to mymidnite.

Last might at 2330 another stopped talking to mymidnite.  I haven't rebooted it yet.  Sometime between last night at 2330 and this morning it also stopped responding to the local status panel application. 

TomW

And the plot thickens....

This refusal to communicate is pesky but I am not sure it is the same fault that makes it reset? Seems most of us do a power cycle to recover and that obviously resets the Classic.

I have had mine blocked from communicating with mymidnite to see if it was part of the issue. It is not. I may start dumping via the USB port and see if that yields some clues.

Ross has mine under constant scrutiny so maybe a pattern will emerge.

Just my current observations.

Tom
Do NOT mistake me for any kind of "expert".

( ͡° ͜ʖ ͡°)


24 Trina 310 watt modules, SMA SunnyBoy 7.7 KW Grid Tie inverter.

I thought that they were angels, but much to my surprise, We climbed aboard their starship and headed for the skies

boB


My Midnite and other communications from the Ethernet port are different, I'm pretty sure, from
the resetting of the Classic itself.

Some of the My Midnite trouble bay be My Midnite itself or in the Classic or of course, both in
some way.

We are still working on the problem.

If the Local App quit communicating with the Classic, make sure the Classic itself is running
and charging batteries, which is its main function, but the communications is very important
too.

boB