s/v Ninaa Ootakii - Winter woes.

Started by Stone, January 13, 2024, 05:44:32 PM

Previous topic - Next topic

boB


On the dead Classic...    Call MidNite Solar at  360-403-7207   and select service I think it is  ?

When you get a moment.   They will want the serial number probably.

boB
K7IQ 🌛  He/She/Me

The Ugly One

Stone-
Have you considered using your auxiliary port on your classic 150. Set it to waste low/waste high. That will allow you to set a voltage point that will trigger the relay. One of them allows you to control a n.c./n.o. relay that has a 12v trigger. Place your relay contactor between your battery bank and the diversion loaders.

Then set your trigger voltage level for the waste high/low as a couple .0 volts above the diversion loader. This way if the system goes into eq mode. It will divert it for a quick minute until the voltage gets raised to the trigger point. Then the relay will disconnect the bank from your diversion loads.
I take them Ray Rays, and turn them into that Boom Boom Zap Juice.

boB

Do you know if the dump loads are (were) working or not ?

K7IQ 🌛  He/She/Me

Stone

Quote from: boB on October 28, 2024, 07:36:03 PMOn the dead Classic...    Call MidNite Solar at  360-403-7207   and select service I think it is  ?

When you get a moment.   They will want the serial number probably.

boB

My classics are fine, I think it's a Chinook dump load controller that is dead.

(The two forward ones tried to dump my entire solar system when the classics went to equalize)
Stone - (s/v Ninaa Ootakii)

8x 265w pv
4x 24v chinook turbines
2x classic 150s
8x L-16s (24v house bank)
8x GC2s (12v convenience bank)