Solar PV system for heating water

Started by asdex, December 15, 2013, 02:38:32 AM

Previous topic - Next topic

asdex

Thanks, yes all this is pretty new to me even though I have had solar panels and regulators on a bus we lived in and then a yacht, it was much simpler. We still use those original Solarex panels. 83 watt and $990 each in 1996. The six 320w panels will be nearly 2kw. I have alot (40 meters) of 16 mm two core TPS I hope to use. I will prefer to site them nearer the house if I can but will have to convince the team of the benefits. (wife thinks they might not be aesthetically acceptable)
But as you say, I'll need to work out the system in total before preceding to do the install.
Cheers,
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North.
12 x 2volt Narada lead carbon batteries (24v 400ah), Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Trimetric monitor, Alibaba solar pump.

stuman

My neighbor uses the dump load to trip a solid state relay when battery voltage exceeds 54 (48 volt nominal system).  He has an electric water heater with 110 volt elements, which run 400 watts plus at 48 vdc.  I want to mirror that, and since my water heater just died, I'm not too far away.

I also have a summer direct type M copper heating array for water, and a wood burner for when nothing else works.  I'm going to relocate the coil next summer, as i relocate my panels for wind protection.


Quote from: asdex on December 15, 2013, 02:38:32 AM
Hi, I'm setting up a solar PV system for heating water. We are off grid and decided we don't want a thermal hot water panel sitting idle for 7-8 months of the year when we heat our hot water with our indoor fire. I'm getting 4-6 320 watt PV panels soon to run a 24 volt system and once I have the details worked out will probibly get a Midnite 150 to gain as much power from the sun as I can then hopefully dump it all to the hot water tank. Anything left will charge the batteries but I already have panels and a wind generator for that.
I'll be following anything about configuring the Midnite Classic and if anyone is heating water with PV panels.
I'm in New Zealand.
Cheer's
Midnite Classic 150, Talesun 240 watt X 15 = 3.6kw.  232 ah 6  volt golf cart batteries x 16 = 464 ah @ 48 volt. MagnaSine 4448 inverter.  Grid connected (as opposed to tied...grid is my backup, but I don't ever feed it).

asdex

Hi, thanks for your reply. Just waiting for my panels to arrive in a couple off weeks then will look at element voltage and get the Midnite 150 controller.
I hope do do the same as the neighbor you mentioned but in reverse so temperature will operate the relay rather than voltage.
I think I'll connect them 3x2 to give 17.22A and 111VMP and change my 12volt battery bank to 24 volts.
Cheers,
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North.
12 x 2volt Narada lead carbon batteries (24v 400ah), Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Trimetric monitor, Alibaba solar pump.

tecnodave

Would someone that is using low voltage water heater elements please point me to the source of these. I am using propane flash boiler heater now but would like to add small pre heater to use excess solar power.

tnx.   td
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P

dgd

Missouri wind and solar amongst others with Ebay stores.
dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

tecnodave

dgd,

Thanks, I will check that out. I do have excess solar power at least 9 months a year and do not like lugging propane bottles to my house.

td
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P

stuman

Quote from: asdex on December 25, 2013, 11:10:00 PM
Hi, thanks for your reply. Just waiting for my panels to arrive in a couple off weeks then will look at element voltage and get the Midnite 150 controller.
I hope do do the same as the neighbor you mentioned but in reverse so temperature will operate the relay rather than voltage.
I think I'll connect them 3x2 to give 17.22A and 111VMP and change my 12volt battery bank to 24 volts.
Cheers,

By doing it the way he does, it is only excess power that heats water.  His primary use of PV power is to charge his batteries and run his fridge/freezer/etc...just like my setup.  I'm currently just building a small wood fire when I want hot water...and I keep a pan on a small propane heater in my bathroom for quick washup warm water.
Midnite Classic 150, Talesun 240 watt X 15 = 3.6kw.  232 ah 6  volt golf cart batteries x 16 = 464 ah @ 48 volt. MagnaSine 4448 inverter.  Grid connected (as opposed to tied...grid is my backup, but I don't ever feed it).

phonetic

Looking to use a 250 litre hot water electric heater.
using 200 litre per day and 45'c temp rise (15 to 60'c) will need 10.7kWh of energy (2.6KW array for 4 peak sun hours)
using 10 250W PVs (Vmpp 30 volts) will give 2.5kW @ 300 volts DC, water heater uses 2.4kW heating element, almost a good match.
use solid state relay & use thermostat from water heater to control.

All I need to do is wait for PVs to get under 60cents per watt, to make it cost effective with heat pump or solar thermal water heater.

Aprox cost $3k with 250 litre storage tank &  10 250W PVs ??
Home:
3.04kW Grid Tie.
Weekender:
6.08kW Off Grid. DC & AC coupled
32 of 190W (12+12 Array DC) (8 Array AC)
Midnite Classic 150 & Classic Lite 150
1.5KW AC coupled Grid Inverter
8 of 600 amp hour Surrette S600 flooded cell battery bank 24 volt 1200 amphour
Outback VFX3024E Inverter Charger, Mate 2.

asdex

My panels will cost $3000 plus element and SSR and should be comparable with a thermal system. Probably a bit cheaper even if I need to buy a PWM controller to divert  to load. With the added advantage of being able to produce electricity if needed, I'm hoping the system will be worth the effort.
We only use about 50 to 80 lts max and I plan to supplement the hot water with some basic water heating devices like solar shower and passive heating systems (copper tubing in glass front box connected to tap)
I have gone for the standard 180 lt cylinder with a wrap to reduce loses.
6 x JA Solar 320w solar panels facing NW, 4 x 300w panels facing North.
12 x 2volt Narada lead carbon batteries (24v 400ah), Classic and WBJr, Epever 50A controller, Outback FX2024 inverter and Mate, Trimetric monitor, Alibaba solar pump.

phonetic

Looking at using a MPPT type DC circuit,  for PVs to charge a capacitor bank & dump to heater element, problems if  not using  MPPT circuit, PV array and heater element will have a very small window of max  power transfer.
Aim is to transfer kWh from PV array to heater element.
Looking to set up a system if total installed cost can be under $2.5-3k
Home:
3.04kW Grid Tie.
Weekender:
6.08kW Off Grid. DC & AC coupled
32 of 190W (12+12 Array DC) (8 Array AC)
Midnite Classic 150 & Classic Lite 150
1.5KW AC coupled Grid Inverter
8 of 600 amp hour Surrette S600 flooded cell battery bank 24 volt 1200 amphour
Outback VFX3024E Inverter Charger, Mate 2.

dgd

Quote from: phonetic on February 16, 2014, 02:51:58 AM
Looking at using a MPPT type DC circuit,  for PVs to charge a capacitor bank & dump to heater element, problems if  not using  MPPT circuit, PV array and heater element will have a very small window of max  transfer.
Aim is to transfer kWh from PV array to heater element.
Looking to set up a system if total installed cost can be under $2.5-3k

Sounds interesting. Capacitor? what type and size?
What about just connecting PVs direct to water heating element?
dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

phonetic

Good example: PV array gets 25% of nominal isolation ie 25% of Impp....as power is proportional to the square of voltage/current for resistance load..will only yield 1/8 of mpp power, but if the array charges a capacitor bank, when capacitor bank gets  charged to Vmpp.. switched to load, the power  duty cycle is approx 25% rather than 12.5%
I hope my ramblings makes sense..maybe the midnite guru's can offer a better example ?
Home:
3.04kW Grid Tie.
Weekender:
6.08kW Off Grid. DC & AC coupled
32 of 190W (12+12 Array DC) (8 Array AC)
Midnite Classic 150 & Classic Lite 150
1.5KW AC coupled Grid Inverter
8 of 600 amp hour Surrette S600 flooded cell battery bank 24 volt 1200 amphour
Outback VFX3024E Inverter Charger, Mate 2.

stuman

One other option to consider is one I'm about to do at home.  I have swapped the 220 elements from my electric hot water heater for 2000 watt, 110 elements.  I have manually connected them directly to my 48 volt battery bank, and they each pull just over 300 watts of 48 volt DC.  Once I get the solid state relays in place, I will automate this at home and never lose another watt.  :)
Midnite Classic 150, Talesun 240 watt X 15 = 3.6kw.  232 ah 6  volt golf cart batteries x 16 = 464 ah @ 48 volt. MagnaSine 4448 inverter.  Grid connected (as opposed to tied...grid is my backup, but I don't ever feed it).