Line and Load from the Classic 150 - Please Help Me Clear this Up ??

Started by Matrix, October 23, 2017, 09:32:13 PM

Previous topic - Next topic

Matrix

I have two MidNite Solar MNEDC breakers.  An 80 amp for the PV coming in.  And a 100 amp for the charge lead going from the CC to the Battery bank. 

Both of the MNEDC breakers have printed on them.   Line on the Top ... and Load on the bottom.   

I assume the wire coming IN from the PV Array is Line,  and it goes out of the 80 amp breaker to the CC as the Load side of this breaker. 

Then coming of out of the CC, Again I assume the Battery + wire out of the controller would go into the Line (top) of the Breaker and the Load would follow on thru to the Battery.    Does this seem correct?   

Is the Battery + side of the Classic 150 the line or the load?? 

Attached is a diagram of what I mean.   

Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Matrix

Here is where it gets confusing to me.   The Classic Owners Manual show just the opposite for the breaker between the Battery and the CC.  The diagram in the Manual has both Red leads of the CC coming off the bottom (load) side of both breakers. 

See Attached. 

Which is correct?  When I called Midnite they did not really give an answer,  simply said that with those breakers they are specific to line side and load side.  And you must connect the Line side to Line and the Load side to Load. 
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

ClassicCrazy

The polarity issue of those breakers has been asked and discussed in other posts.
The MNEDC breakers that have the studs on them you can wire up either way - there is no polarity on them even though the label says Line and Load .  Same thing with the big inverter breaker.
The din rail mount breakers with the screw clamps are polarity sensitive though and those have a + marking at the bottom of them.

There are lots of posts on forums about this if you go to main page and do a search.
Here is one
http://midniteftp.com/forum/index.php?topic=483.msg2874#msg2874

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

Matrix

Quote from: ClassicCrazy on October 23, 2017, 10:28:00 PM
The polarity issue of those breakers has been asked and discussed in other posts.
The MNEDC breakers that have the studs on them you can wire up either way - there is no polarity on them even though the label says Line and Load .  Same thing with the big inverter breaker.
Thanks Larry.  Is the lead coming off the CC,  would that be considered a Line ... or a Load? 

Quote from: ClassicCrazy on October 23, 2017, 10:28:00 PMThe din rail mount breakers with the screw clamps are polarity sensitive though and those have a + marking at the bottom of them.
Are those breakers AC or DC.   I have the din rail ones too for my AC Loads ... but they are AC not DC.  Does the Plus Marking indicate Line or Load?   
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

ClassicCrazy

Yeah I was talking about the DC breakers - not AC .
I just added a link to my first post reply - read that one
Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

ClassicCrazy

I like to use this wiring diagram from the Midnite Mini DC Disconnect box
You can just ignore the two breakers shown for the ground fault device ( 63 and 5 amp side by side )
So for your question on the din rail breakers it shows them with the + being at bottom and that is where the battery and the PV would go. But for the other type DC breakers with the studs it wouldn't matter which stud  you wired them to - no polarity .


Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

Matrix

OK so that clears up the DC side,  but what about the AC side.  I have both and AC out and an AC in to and from my inverter.  Again the wiring diagram that Came with the MidNite Solar E-Panel for the Schneider Inverter has both the AC in and the AC out going to the top of the Breakers (they are both double pole 30 amp MNEAC 30-2P).    Can this be right?  I have them wired that way now,  it is working,  and it does disconnect things.  But It may have no protection. :(   I called Midnite a few weeks ago and  I think  I recall them telling me that the AC does not matter.   
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

Matrix

Quote from: ClassicCrazy on October 23, 2017, 10:59:46 PM
I like to use this wiring diagram from the Midnite Mini DC Disconnect box
You can just ignore the two breakers shown for the ground fault device ( 63 and 5 amp side by side )
So for your question on the din rail breakers it shows them with the + being at bottom and that is where the battery and the PV would go. But for the other type DC breakers with the studs it wouldn't matter which stud  you wired them to - no polarity .


Larry
Your posted diagram is the opposite of what i have for DC ... but from the link you posted,  it does not matter correct?
Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install

ClassicCrazy

In regards to the AC  - I have not used those types of Midnite AC breakers but if you look at the spec sheet carefully it tells which types of breakers are polarity sensitive.

http://www.midnitesolar.com/documents.php?productCat_ID=16&productCatName=Breakers&model=MNEAC-2P%2015A%20thru%2025A&product_ID=190&act=

And if you called Midnite and asked them and they said they were not polarity sensitive I would go with that advice as well.

For the DC it only matters which side of the breaker it goes to if it is the Din rail type.

Larry

system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

Resthome

John

10 x Kyocera KC140, Classic 150 w/WBJr, Link10 Battery Monitor, 850 AH @ 12v Solar One 2v cells, Xantrex PROwatt SW2000
Off Grid on Houseboat Lake Don Pedro, CA

Matrix

Grid-Assist Off-Grid
REC TwinPeak 2 285W 3S-3P 2565w-STC 1926w-NMOT Array / Classic 150 / Conext SW 4024 Inverter
Trojan L16H-AC 435Ah bank 4S  with 7' of 4/0 cable
24 volt system /  Need 3200Whs Daily
My System Install