Rolls surrette batteries

Started by russ_drinkwater, December 02, 2015, 05:56:03 AM

Previous topic - Next topic

russ_drinkwater

I have been offered a 24 volt bank of brand new rolls batteries 1330 or 1350 amp hours, not sure atm.
The problem is these batteries have been wetup for over 12 months without a substantial charge.
Would they be toast or usable.
I am concerned about stratification in the cells as well as sulphation.
Should I leave them alone?
The cost is $3,000 and I can not afford to have duds.
Ideas please.
Russ
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

Halfcrazy

Well here are my thoughts:

1- Probably there will be no warranty do to the lack of charge? (I would call surrette and ask)
2- They may be sulfated? (Again I would ask Surrette there thoughts on these sitting for 12 months)
3- The same size bank of say Trojan L16s would be about $5,000

Personally I would tend to NOT buy used batteries unless they where a screaming deal or I was SURE of the history.
Changing the way wind turbines operate one smoke filled box at a time

russ_drinkwater

The batteries are brand new and at a Rolls retailer!
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

Vic

Quote from: russ_drinkwater on December 02, 2015, 05:56:03 AM...
...   The problem is these batteries have been wetup for over 12 months with a substantial charge.
Russ

Hi Russ,

Try as I might,  cannot process the sentence in the above quote.

Is "wetup"  setup?   Or have they been murdered?   And,  the reference to "substantial charge",   is  a bit unclear.

Was this part of a Demo system at the dealer,  and had been kept charged,  perhaps on Float  ??

Do you know when these batteries were made?  Depending upon the model battery,  there are normally Date Codes on the Flag terminals of the 5000 series Surrettes,  and often on the case on the 4000s.

Roughly,  how deep is the discount being offered,  compared to what you could buy fresh batteries for?

Thanks,  Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Halfcrazy

Well if they are at the distributor than I would assume they cary full warranty and have been maintained while there
Changing the way wind turbines operate one smoke filled box at a time

Westbranch

Quote from: Halfcrazy on December 02, 2015, 08:00:14 PM
Well if they are at the distributor than I would assume they carry full warranty and have been maintained while there

Best to get it in writing!
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

russ_drinkwater

The batteries have had acid in them for over 12 months now (ie.wetup as opposed to dry!)
They charge $900 for each 4 volt cell retail and they offered them to me for $500 a 4 volt cell (could be 2 x 2 volt cells in a poly tub as I have not seen them yet!)
So $3,000 cash is my buy price as opposed to $5,400 plus 10% gst.
For the same money( $3,000) I can get 12 trogan T105's 225 amp hours @ 6 volts.
So the trojans would be 24 volts @ 675 amp hours as opposed to the rolls at 1330 amp @ 24 volts.
I am in australia so things are a lot dearer here!
I was going to take my hydrometer and amp/volt meter with me and if the cells have a sg under 1.240 my thoughts are to forget them?
Just do not know what to do.
HELP!
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

Westbranch

What are they offering for Warranty? If they will stand behind them for X months (>24?) they must have faith in them, otherwise you re buying a lot of potential scrap lead...

Ask them if they will load test them while you are present... if they flinch..... they may be hiding something...

KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

Hi Russ,

OK on the "wetup",  this must be down-under slang ...   have heard of things that have dried up,  but never heard of wettingup,  especially as one word.

And,  if these are Surrette 4KS25  --  1350 Ah four volt batteries,  then,  you can buy new ones for about about 67%m  or so of what we pay for them in the USA.

It really all depends upon how these batteries were treated at the dealer.  Also,  the "more than 12 months",  can be a bit troubling,  as this could be 15 years,  or so ...

Load tests need to be done carefully with batteries of unknown background,  as,  irreversible damage can occur if one is not careful.

Would suggest measuring SG of each cell,  as well as each battery's voltage,  before doing any load test,  and then,  carefully monitoring the battery voltage during any discharge test.

Seems like a good price,  especially if there is a full Factory warranty which is 3/10  years in the USA.

Good Luck,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

russ_drinkwater

Thanks for the replies. There is no mention of warranty on the cells. I have contacted Rolls and they said that the warranty would have to be worn by the dealer and the dealer is not offering warranty. So in that case I think I will steer clear of them unless they are a lot cheaper than 3k and I can test specific gravity and voltage as well.
I have talked to a local trojan dealer and I can get 16 x 6 volt t 105's 225 amp hour for $3520 ($220 each)
So I am going to go that way.
900 amp hours of storage and I will be taking less than 20% off them before switching back to mains at night.
With the 20 x 220 watt panels on most days I will have 100-150 amps at 24 volts going into them and most times I would never be drawing 10-15 amps at 240 volts out of them. So the arrays should keep them topped up well except for cloudy days.
The system is just a backup on part of the house for summer storms and blackouts.
I am a greedy turd as well, because we have 15kw's of grid tie systems here and I am trying to get as much back from the power companies as I can before my 44 cents per kw buyback tariff finishes.
The power company is paying for my standalone batteries as our grid tie systems have paid for themselves at the end of last year.
Sorry I just hate power companies and government the way they screw people over power and water etc.
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

Halfcrazy

I think you are making a wise choice. A reputable distributor would have maintenance records on them to satisfy Surrette so the warranty would be in full force. The fact they dont offer a warranty tells me they never took care of them for "more than 12 months"
Changing the way wind turbines operate one smoke filled box at a time

russ_drinkwater

The distributors never got back to me last week, so that means the batteries have been sold to some poor soul
for 6 X $900= $5,400. (Their retail asking price)
Oh well it was not me and that is all that matters. lol.
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

russ_drinkwater

I bit the bullet and bought some trojan L16's.
Just 4 to start with and when I get a bit more cashed up I will add another 4 to the bank.
They cost $680 australian a battery, not sure what the retail is on them in the US.
Pick them up on monday.
Oh, on another note the system they quoted on did not go ahead so they still have the rolls batteries in their warehouse, lol.
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

russ_drinkwater

Just an add note. Have had the trojans hooked up and working now for over 3 weeks. The system as it stands during the day runs 2 large fridges and 2 freezers (1000 liters between the two) and late arvo I switch the 2 fridges and the 800 liter freezer back to grid feed. The midnite reg does its job flawlessly and the batteries have not required any water addition in the 3 weeks. I guess they are not working that hard. The voltage in the morning is 25.1 volts before sunrise. The reg spends most of its time in float after approx 9am.
Anyone have the L16 batteries and can give me an idea what the best equalize regime is? Or just follow the trojan guidelines?
Standalone. 20 Hyundai x 220 watts panels, 2 x classic 150's, Latronics 24 volt 3kw inverter, Whiz bang Jnr, 12 Rolls surrete  4KS 25P  batteries and WBJ.
Grid tie feed-in, 12.5 kw in 3 arrays generating 50 kws per day average. Solar river grid tie inverters

tecnodave

Russ,

I bought my set of Interstate L-16's for $208USD ea. retail seems to be about $275 ea here in California. Trojans L-16 here are about $320 ea USD when bought in sets. (6 volt 400 a.h.)

Hope this info is of use to you.....shipping is the whopper!

David