Default Settings For Kid Battery Bank

Started by Free Energy Freak, July 17, 2014, 07:38:46 PM

Previous topic - Next topic

Free Energy Freak

I have batteries that I am unable to secure the proper charge parameters for. So, I would like to use default parameters.


So far, I am thinking:


Absorb at 14.4
Float at 13.6 (or should that be 13.8?)


What about EQ and Bulk? What should they be set at, please?
400 watts, MS ProStar 30m, 12vdc @ 240 AH - Internal lighting & 12v Shurflo pump at farm.
270 watts, Beta Kid, 12vdc @ 120AH - Back up internet, computer, during weekly power cuts.
100 watts, MS Sunlight 10a, 12vdc @ 50AH - Exterior LED perimeter lighting at farm.

Westbranch

what type of batteries are they ? AGM ? FLA ? Gel ? Traction? etc.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Free Energy Freak

400 watts, MS ProStar 30m, 12vdc @ 240 AH - Internal lighting & 12v Shurflo pump at farm.
270 watts, Beta Kid, 12vdc @ 120AH - Back up internet, computer, during weekly power cuts.
100 watts, MS Sunlight 10a, 12vdc @ 50AH - Exterior LED perimeter lighting at farm.

chris

  what brand and model are the batteries?
System 1
12 volt system,
280 AH DIY LifePO4 with 200amp JBD BMS
4x200 Watt 36volt panels 4P
MidNite Kid, WBjr
2000 watt Kisae SW inverter

System 2
Off Grid RV (parked and used as a cabin)
12 volt system,
4 X T-105+
6X100 watt array wired as 3 strings
MidNite Kid, WBjr & MNBTS
1500 watt Cotek SW

Free Energy Freak

#4
Quote from: chris on July 17, 2014, 08:17:15 PM
  what brand and model are the batteries?

A generic brand from Taiwan. 120AH is all I know.. No paperwork, no nothing. That is why I want to go with the default settings for my Kid, please.


If it helps, it is a Beta Kid, with all options offered by Midnite - Temp sensor, Whizbang, shunt.
400 watts, MS ProStar 30m, 12vdc @ 240 AH - Internal lighting & 12v Shurflo pump at farm.
270 watts, Beta Kid, 12vdc @ 120AH - Back up internet, computer, during weekly power cuts.
100 watts, MS Sunlight 10a, 12vdc @ 50AH - Exterior LED perimeter lighting at farm.

Vic

#5
Crap  !!!   Timed out again ...


HI F E F,

Good that they are FLAs,  so you can measure how well the batteries are getting charged.

Agree with 14.4 Vabs to start with.  Adjust the time or EA to fully charge the bank.  Increase the Vabs to fully charge the bank.

Would guess 13.25 V for Float.   Most say that you want to just barely maintain SG with the Vfloat you choose ...  you can measure how well this setting does that by measuring SG after a few hours in Float.

My opinions and guesses.  YMMV.   Good Luck,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Free Energy Freak

Thanks. And, God, I hate it when it times out, as we have discussed before.

Um, anyone have input on EQ and / or Bulk voltages?

EQ, possibly 15.0v for 1.5 hours?

Should (Could?) Bulk be the same as Absorb, at 14.4v?
400 watts, MS ProStar 30m, 12vdc @ 240 AH - Internal lighting & 12v Shurflo pump at farm.
270 watts, Beta Kid, 12vdc @ 120AH - Back up internet, computer, during weekly power cuts.
100 watts, MS Sunlight 10a, 12vdc @ 50AH - Exterior LED perimeter lighting at farm.

vtmaps

Quote from: Free Energy Freak on July 18, 2014, 02:46:14 AM
Should (Could?) Bulk be the same as Absorb, at 14.4v?
There is no bulk voltage setting.  During bulk, the kid pushes as many amps as it can into the battery, and the battery voltage rises.  When the voltage rises to the absorb setting, the bulk stage of charging is over and the kid throttles back its output current so the battery does not go over the absorb setting.

--vtMaps

Free Energy Freak

Thanks.


Okay, so, settings for the Kid, for an "unknown" battery:


Bulk = Automatic
Absorb = 14.4vdc
Float = 13.25vdc
Equalization = 15.0vdc


Thanks to all for helping me sort this.


I still have to wait another day for the concrete to cure. Then, I will start mounting the panels and work on the rest of the installation.
400 watts, MS ProStar 30m, 12vdc @ 240 AH - Internal lighting & 12v Shurflo pump at farm.
270 watts, Beta Kid, 12vdc @ 120AH - Back up internet, computer, during weekly power cuts.
100 watts, MS Sunlight 10a, 12vdc @ 50AH - Exterior LED perimeter lighting at farm.

Westbranch

do you have a generator to bulk the battery to prep for an EQ?
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

Quote from: Free Energy Freak on July 18, 2014, 11:09:11 AM
Thanks.


Okay, so, settings for the Kid, for an "unknown" battery:


Bulk = Automatic
Absorb = 14.4vdc
Float = 13.25vdc
Equalization = 15.0vdc

F E F,  Generally,  EQ @ 15 V is TOO LOW.   Would raise this to a minimum of 15.5 V ...  unless your Inverter (or connected DC loads)  will not tolerate  a voltage above this.

Sometimes,  with cool batteries,  this voltage can rise above the Max for the inverter of DC loads connected to the batteries ...   FWIW,  more opinions.  Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

Free Energy Freak



Quote from: Westbranch on July 18, 2014, 11:32:40 AM
do you have a generator to bulk the battery to prep for an EQ?

No, unfortunately.
400 watts, MS ProStar 30m, 12vdc @ 240 AH - Internal lighting & 12v Shurflo pump at farm.
270 watts, Beta Kid, 12vdc @ 120AH - Back up internet, computer, during weekly power cuts.
100 watts, MS Sunlight 10a, 12vdc @ 50AH - Exterior LED perimeter lighting at farm.

Free Energy Freak

Quote from: Vic on July 18, 2014, 12:03:04 PMF E F,  Generally,  EQ @ 15 V is TOO LOW.   Would raise this to a minimum of 15.5 V ...  unless your Inverter (or connected DC loads)  will not tolerate  a voltage above this.

Sometimes,  with cool batteries,  this voltage can rise above the Max for the inverter of DC loads connected to the batteries ...   FWIW,  more opinions.  Vic

Okay.

I can disconnect loads during the day. We only really need to have the loads connected at night. Only once in a while do we need anything running during daylight hours. That would be a pump, but only for a little while.

And, cool or cold will not be happening here I am pretty sure. We are at 13 degrees North Latitude. :D
400 watts, MS ProStar 30m, 12vdc @ 240 AH - Internal lighting & 12v Shurflo pump at farm.
270 watts, Beta Kid, 12vdc @ 120AH - Back up internet, computer, during weekly power cuts.
100 watts, MS Sunlight 10a, 12vdc @ 50AH - Exterior LED perimeter lighting at farm.

Westbranch

I forget how much PV  (W) you will have?  If not a good sized array for the batteries you may not get to EQ without a genset (or grid). 

You have to be fully charged before you can do an EQ.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Free Energy Freak

#14
Quote from: Westbranch on July 18, 2014, 07:46:59 PM
I forget how much PV  (W) you will have?  If not a good sized array for the batteries you may not get to EQ without a genset (or grid). 

You have to be fully charged before you can do an EQ.

This array will be 270 watts (2-135 watts panels), at 24 volts into the Kid. Out to a single 120 AH, 12vdc battery.


I will make sure I wait for a good sunny day, prior to going to EQ.
400 watts, MS ProStar 30m, 12vdc @ 240 AH - Internal lighting & 12v Shurflo pump at farm.
270 watts, Beta Kid, 12vdc @ 120AH - Back up internet, computer, during weekly power cuts.
100 watts, MS Sunlight 10a, 12vdc @ 50AH - Exterior LED perimeter lighting at farm.