alphagen dcx3000 for charging

Started by new2PV, May 12, 2015, 08:36:28 AM

Previous topic - Next topic

new2PV

Could you use this generator to charge a 48 volt battery bank?  Could you connect it to a classic 150.  Would it damage the inverter?

Specs below?
http://www.alpha.ca/web2/products/generators/item/alphagen-portable
Zahn inverters SOLD, looking for something new..

mike90045

My first guess is NO, it won't work.  Even wired directly to the batteries.

A 48V telcom DC power source, does not have the 60V output needed to recharge 48V batteries, you need a higher voltage than the battery, to push power into the battery.

Quote"48V: ................................52.5Vdc nominal at generator output connector"
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

new2PV

The unit is designed to maintain the batteries, not charge them.  In an emergency situation you would have power and not deplete your batteries, but they wont get charged either.