Does Midnite Solar make an outside rated DIN railed Baby Big Box? I want to house two 150vDC breakers outside near the PV arrays. Or...what is the smallest/least expensive option do I have for a small weather resistant breaker box? Thanks.
Chris
MNPV3 i think it is called. 3 breaker combiner.
P.
That is correct the MNPV3 is a 3 spot din rail box and the MNPV6 is the 6 spot outside box
Roger that...thanks guys.
Quote from: Jacotenente on December 14, 2015, 10:03:53 PM
Does Midnite Solar make an outside rated DIN railed Baby Big Box? I want to house two 150vDC breakers outside near the PV arrays. Or...what is the smallest/least expensive option do I have for a small weather resistant breaker box? Thanks.
Chris
Please excuse my ignorance. If you mounted this disconnect near the PV arrays, wouldn't someone (fireman?) think it was a master PV disconnect? From the manual:
QuoteFuses are available from 1 to 30 amps. (...) Use MidNite Solar 1000 Volt fuses. These devices are not polarity sensitive, but do not open them under load. You
WILL have a fire on your hands!
I'm looking for a exterior, pole mounted disconnect that would not arc-over/self destruct if the breakers were thrown under high-amp, DC voltage. What relatively low-cost options would you use?
In our older system, we shutdown the system outputs first and then proceed back to the input disconnects ....