Power sag when turning generator off.... how dangerous to electronics?

Started by alyaz, January 29, 2017, 12:02:59 PM

Previous topic - Next topic

alyaz

We have a Magnum inverter.  Although we generally try to manually turn the generator off when no electrical items are in use, there has been occasion that the generator will turn off and the lights (and if the TV were on it may even turn off) will dim before the inverter restores battery power.

So my question is, it is usually this ‘power sag’ that is so dangerous for electronics, right?  If so, should a person have a ‘surge protector’ like one of the “Progressive’ units to turn power off to an expensive fridge etc?

Thanks...
3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

Westbranch

Sounds to me like the 'transfer switch speed"... is too slow

mine for Utility to Inverter is 16 - 50 msec,  faster in reverse Inverter to Utility, 8 - 10 msec
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

alyaz

Sorry, should have mentioned we are ‘off grid’, so no utility tie here...  Or am I not understanding you correctly?  Thanks.
3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.

mike90045

Actually, you need to check your Generator Qualification settings.
It sounds like as the generator slows down, it's still being held onto by the Magnum.
There should be settings for both Frequency and Voltage, as a window, of what is acceptable to the Inverter (or ]you)
Fq  55-65 Hz
voltage 220 - 250 VAC 
or something like that.
  Your eyeball can see even a small variation of voltage as dimming (I used to drive the Power Quality folks at my plant mad, I'd call them and ask, what happened?   Dropped 2 cycles as a transformer tap stuck or something.  They could not believe that I, sitting at my desk, can call and report stuff their gear didn't alarm on, and be right every time.)

What you NEVER want to have happen, is the loads to stay connected as the generator winds down and stops.  This will REMOVE the residual magnetism in the rotor, and it will stop generating.  There is a fix:
http://www.dieselduck.info/machine/03%20electricity/flashing_generator.htm
http://tinyurl.com/LMR-Solar

Classic 200| 2Kw PV, 160Voc | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph )| Listeroid 6/1, st5 gen head | XW6048 inverter/chgr | midnight ePanel & 4 SPDs | 48V, 800A NiFe battery bank | MS-TS-MPPT60 w/3Kw PV

Westbranch

AL, in my case I am OG too, and 'utility' = Generator, stop gen and it switches to battery... :)
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

Vic

Hi Al,

Looking at the specs for the Magnum PAE Inverters,  they do "spec" 16 ms Transfer speed,   although there are no limits speced  (ie Max,  or Typical),   just that specs are at 25 C.

The Magnum inverter line have  a reputation of not being particularly fast at regulating voltage,  which could be part of the issue.

FWIW,   Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

alyaz

Thanks for all the replies.

I do recall speaking to someone at Magnum a few years ago about this issue.  They told me there was an updated ‘board’ available that should help somewhat, but I think it was about $400 or something to that effect.

Regards,
Al
3.3 kW solar. (1.5 kW Helios - MN Classic 150 CC; .8 kW CSun - MN Classic 150 CC; 1 kW Sharp - MN  Classic 250 CC); Magnum PAE-4024 Inverter, AGS, ARC, BMK. Whizbang Jr., Midnite Solar battery monitor, 5 Midnite SPD’s. 24V Rolls 4KS21P - 1105 a/hr FLA.  10 kW Perkins Diesel.