Greetings

I am working with Doctors Without Borders (MSF).

Since MSF uses mostly seal batteries could anyone suggest to me a good test for sealed batteries to reveal their true health. It seams that there are allot of 220Ah ish @12V batteries in the different missions using older Xantrex, Victron and a few OutBAck Inverter/Chargers as a backup when the gen or the unstable grid goes down. Would there be some kind of simple load test that you could share with me?

Marc

ClassicCrazy

Not sure there is a simple load test. A load is a load - even if it is a bunch of resistors. You need to log certain amount of amps for amount of time and see what happens to the voltage.

If I was testing them I would put a large load on them and see if the voltage takes a dive. Then go down lower in amps and see where the battery will deliver the most amount of amps for the longest time and that would give you an idea of what it is capable of.  And if they are in series and one of them is not so good then you will have some problems .

There are meters that are supposed to be able to test the capacity . The fire alarm testers would put those on AGM batteries and it would give a reading of capacity - maybe using internal resistance. But I never trusted those since a new battery would read the same as an older one and also seemed like two of the same kind meters would give different readings.

Larry
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

Westbranch

here is a document for testing  my brand of batteries, should be basically the same for all brands
http://www.cdtechno.com/pdf/ref/41_7135_0412.pdf

here is the link to all their documents some good additional reading

http://www.cdtechno.com/resource/support_doc.html

hth
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

ClassicCrazy

Quote from: Westbranch on February 09, 2017, 08:44:01 PM
here is a document for testing  my brand of batteries, should be basically the same for all brands
http://www.cdtechno.com/pdf/ref/41_7135_0412.pdf

here is the link to all their documents some good additional reading

http://www.cdtechno.com/resource/support_doc.html

hth

They sure have some good documentation and instructions .
system 1
Classic 150 , 5s3p  Kyocera 135watt , 12s Soneil 2v 540amp lead crystal for 24v pack , Outback 3524 inverter
system 2
 5s 135w Kyocero , 3s3p 270w Kyocera  to Classic 150 ,   8s Kyocera 225w to Hawkes Bay Jakiper 48v 15kwh LiFePO4 , Outback VFX 3648 inverter
system 3
KID / Brat portable

Westbranch

Hi Larry.

Yes, and their paper on charging is very informative... good all-round knowledge.
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

WindFarmer

Thanks guys for the information. I will check it out.

Paix, Marc

niel

if the batteries are sunxtenders or lifelines batteries go to the concorde battery website and read up on how they recommend doing it.

russ_drinkwater

Also with smaller batteries look for physical deformities, ie. bulges, general swelling in battery housing.