General Category => System Design and Layout => Topic started by: jramerman on June 06, 2020, 03:57:31 AM

Title: Connecting PV Arrays through Breakers
Post by: jramerman on June 06, 2020, 03:57:31 AM
Greetings all. I am just wondering if I have correctly connected my 2 PV arrays to a Classic 150 via 2 x breakers. Attached is a diagram of the connections up to the Classic 150. The diagram explains the equipment involved.
Title: Re: Connecting PV Arrays through Breakers
Post by: ClassicCrazy on June 06, 2020, 10:43:53 AM
The way I do it and most combiner boxes is to have each array positive go to it's own breaker . The two positive breakers feed into a common wire  that goes back to the controller that has another breaker sized for that  wire. The negative  goes direct to controller with no breaker .

So PV one to 15 amp ( or 20 depending on wire size and array)   PV two to another 15 amp . The two positive  breakers feed into 6 gauge wire ( for maximum power input my classic can handle )  . That six gauge goes to 60 amp breaker that feeds the Classic. The two array negatives are tied together in combiner box with 6 gauge and go directly to Classic negative input .
There is more info and schematic here http://www.midnitesolar.com/pdfs/MNPV_Instructions_Rev_A.pdf

Larry
Title: Re: Connecting PV Arrays through Breakers
Post by: mike90045 on June 06, 2020, 01:05:04 PM
I'll vote for using a std combiner box, not cobbling something together.
http://www.midnitesolar.com/productPhoto.php?product_ID=77&productCatName=Combiners&productCat_ID=9&sortOrder=5&act=p
Title: Re: Connecting PV Arrays through Breakers
Post by: jramerman on June 08, 2020, 05:23:01 AM
Thank you ClassicCrazy and Mike 90045 for your input. Regards.