step down converter

Started by opticalmike, June 18, 2014, 10:20:16 PM

Previous topic - Next topic

Westbranch

If you put all 6 in series you will be WAY over the sweet spot as Dave put it. 
Why? because you have the formula wrong, in series configuration you add the voltage ONLY , in Parallel configuration you add the Amps.
So in your case you will have a nominal Voltage of 6 x 12v = 72V nominal, Voc much higher.
A ratio of 6:1
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

vtmaps

Quote from: opticalmike on June 25, 2014, 02:54:41 PM
would it be better to just go with 2 more 85's and run all 6 panels in series
4.93 x 6 = 29.58 amps
Putting 6 of those 85 watt panels in series will mean multiplying the VOLTAGE by 6.  The current will be 4.93 amps.

Why don't you do what I suggested back in reply #6 in this thread:
QuoteYou can keep your old panels and controllers as they are, and add a kid and new panel.  No problem having multiple controllers all charging the same battery.

--vtMaps

vtmaps

Quote from: opticalmike on June 25, 2014, 02:54:41 PM
would it be better to just go with 2 more 85's and run all 6 panels in series
4.93 x 6 = 29.58 amps

If you want to run six of those 85 watt panels, you could put them all in PARALLEL with your current controller (if it can handle the 29.58 amps... you haven't told us what controller you have).  Your combiner would need six circuit breakers.

You could also hook up the six 85 watt panels in three parallel strings (with two panels in series per string).  In this case you would be combining three strings and your current circuit breakers would be OK.  You would need an MPPT controller such as the kid.

--vtMaps

tecnodave

Vt,

I did not recommend that course due to the fact that his existing controller is a Chinese PWM  controller. When the kid pulls up the voltage to a true charge for t-105's it will cause the Chinese controller to shut down as it will see a "full battery" . I have this situation with my Chinese Tracer MPPT controllers on same battery with a kid or Classic. I can use my Tracers to assist with bulking, but at adsorb they shut down, leaving all the work to the controllers that can be tailored to the battery type.

This is exactly what I am referring to when I say  "1 size fits all"  , most Chinese controllers assume a group 27 auto start/deep cycle , there is no provision for a true deep cycle such as T-105's , GC-2's , and L-16's.

My opinion on batteries that have a listed CCA (cold cranking amps) : this is not a "true deep cycle" it is an auto start battery! Not suitable for solar work! It will not stand the repeated cycling found in RE systems and will fail in 90 days or so.

To mimic TomW,  that is my story and I'm sticking with it.

td
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P

tecnodave

Optical mike,

I may have misidentified wires in your converter box,  going back to the pic's you posted there are two stranded wires in that converter box. On #5 breaker there is a stranded wire going to the bottom portion of the converter, this one is probably the AC to DC converter power, I'm not sure just what the other stranded wire is. Trace it back and see if it exits the back of the box or stays inside. This is on the water heater breaker and might  power the transfer relay. There are two open breaker spots and you could easily add one SquareD Homeline HOM1515CP breaker to separate the circuits. The relay when energized makes a clack sound as the relay switches.

td
#1 Classic 150 12 x Sharp NE-170, 2S6P, 24volt L-16 Rolls-Surette S-530, MS4024 & Cotek ,  C-40 dirv.cont. for hot water
#2 Classic 150 12 x Sharp NE-170, 2S6P, 24 volt L-16 Interstate,Brutus Inv.
#3 Kid/WBjr 4/6 Sanyo 200 watt multilayer 4/6 P
#4 Kid/WBjr 4/6 Sanyo 200 watt multilayer 2S 2/3 P

opticalmike

Quote from: dgd on June 25, 2014, 02:21:45 PM
Mike,
Your original first post in this thread is the way to go. Hanwa panel would be good and rewiring the 85w PVs for 24v. Then the two 24 volt strings of 85s and the hanwa, at 24 volts, can wire into you midnite combiner using  3 breakers.
The answer to your question is that the KID will be perfect for this setup and will do all the voltage down conversion to charge your 12 volt battery bank.

Dgd
would I still be able to use my 12 volt inverter?
mike

Vic

Mike,

Think that the rub in dgd's suggestion,   is that when you mentioned that the Hanwah PV was 24 V,  it is NOT really a 24 V PV.   td did mention this fact previously.   Almost all PVs in the 230 - 275 W range are 60 cell.   Many folks call these PVs 24 Volters,  but the Vmp of this PV is just under 30 V.  A REAL 24 V PV has a Vmp of about 35.5-ish Vmp.  Some will be a bit above 36 Vmp.

As such,  strings of two of the real 12 V 85s will not get along well with 30-ish V Vmp PVs,  like the Hanwah.    FWIW.  Vic
Off Grid - Sys 1: 2ea SW+ 5548, Surrette 4KS25 1280 AH, 5.25 KW PV, Classic 150,WB, Beta Barcelona, Beta KID
Sys 2: SW+ 5548s, 4KS25s, 5.88 KW PV, 2 ea. Classic 150, WB, HB CC-needs remote Monitoring/Control, site=remote.
 MN Bkrs/Bxs/Combiners. Thanks MN for Great Products/Svc/Support&This Forum!!

dgd

Ahh, the danger of making assumptions  :(
Having goooggledd the hanwha PVs they all appear to be the 60 cell type so my original suggestion about using one is completely wrong.
Thanks for pointing out this info Vic..

Mike, your suggestion about getting another two 85W pvs looks good.
I would suggest wiring each two in series (ie connect positive from one panel to negative on other then remaining +ve and -ve go to junction box).
So you have three sets of wires going to junction box.

This would mean about 35volts at 14.5A going to KID, ideal for mppt to charge a 12v battery.

Your 12v inverter connects to battery and is not effected by how you configure the PVs into the KID.

dgd
Classic 250, 150,  20 140w, 6 250w PVs, 2Kw turbine, MN ac Clipper, Epanel/MNdc, Trace SW3024E (1997), Century 1050Ah 24V FLA (1999). Arduino power monitoring and web server.  Off grid since 4/2000
West Auckland, New Zealand

opticalmike

I did manage to get two more 85 watt panels, so if I rewire them into 3 strings of 2 panels what about the 10 amp breakers I have?....do I need to buy the 15 amp breakers?
KID and temp probe and Wbjr and shunt...on their way
These are the panel specs:
Vmp 17.3v
Imp  4.93a
Voc  21.6v
Isc   5.28a
Location Northern Alberta
winters ~ -40C
what would the final voltage be on a cold winter day...we see lots of these!
thanx,
mike

Westbranch

If you use the sizing tool for which ever CC you are going to get it will tell you how high V cold will get for your desired temp...

KID   http://www.midnitesolar.com/sizingTool_kid/index.php

Classic  http://www.midnitesolar.com/sizingTool/index.php
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

chris

  I believe the kid is rated for 150 volts......so I don't think you have anything to worry about there.....I'm not in northern alberta.....but here in the Kootenays BC I didn't have any problems.

  Besides....running them in stings of 2 will only bring you up to 34.6 volts
System 1
12 volt system,
280 AH DIY LifePO4 with 200amp JBD BMS
4x200 Watt 36volt panels 4P
MidNite Kid, WBjr
2000 watt Kisae SW inverter

System 2
Off Grid RV (parked and used as a cabin)
12 volt system,
4 X T-105+
6X100 watt array wired as 3 strings
MidNite Kid, WBjr & MNBTS
1500 watt Cotek SW

opticalmike

whats better? I dont use in winter at all. 6 in series, 2 strings of 3, or 6 in parallel? is it better to have more amps or more volts?

Westbranch

Assumption:  I believe you are wanting a 12 V b. bank...(?)

So, how efficient or, contrarily, how inefficient do you want the system to be?

The larger the difference of the V going into the CC and the V coming out of the CC determines both!

The recommended difference is to go from one step ie 24 V to the next lower step, ie 12V,
or 48V to 24V... or 96V to 48V.

So in your case you are going from 6 x 17.3 =103.8V too much differential to 12 V
3 x 17.3 =51.9  ... better
2 x 17.3 = 34.6 .... better still
1 x 17.3= 17.3 ...  best for 12 v system

Then you have to consider the distance between the array and the b. bank and the line losses.
I believe you are talking about a camper/trailer so losses may be small, now the kicker:  the higher the V, the less loss per foot or meter that Voltage has to travel between the panel and the battery... so you trade one efficiency for another loss.

here is a voltage drop calculator you can use

http://www.solar-guppy.com/download/voltage_drop_calculator.zip
KID FW1811 560W >C&D 24V 900Ah AGM
CL150 29032 FW V.2126-NW2097-GP2133 175A E-Panel WBjr, 3Px4s 140W > 24V 900Ah AGM,
2 Cisco WRT54GL i/c DD-WRT Rtr, NetGr DS104Hub
Cotek ST1500 Inv  want a 24V  ROSIE Inverter
OmniCharge3024  Eu1/2/3000iGens
West Chilcotin 1680+W to come

opticalmike

My panels are less than 20 ft to the cc and battery bank
Loss on wire is less than 2 % so highest amperage ?
I need 2 more 10 amp breakers 

Westbranch

Highest amperage  would be 6 x 4.93A = 29.58A from combiner to CC, and depending on what the CC sends to the battery, there could be  a (modest) boost in amps depending on battery SoC.

hth