Changed from 2 x 12v 100ah AGM to 2 x 12v 100ah Lithium. Reset Kid to Lithium, 12V etc. Enabled WBJ. Shows 100% SOC (correct) but 400ah instead of 200.
>>>>>>>> Solved, boB reminded me to set WBJ parameters after the reset >>>>>>>>>>>
After re-starting or booting a powered down Classic, it will assume 100% state of charge except that it is not confirmed until the first Absorb to Float transition. This assumes that Absorb time and voltage are programmed correctly as well as amp-hours battery capacity and amp-hour charge efficiency.
Have you gone to the Whizbang-Junior setup screen(s) and adjusted these parameters ?
From the main status screen, press STATUS until you hit that screen. It is 2 or 3 screens away from the first status screen.
There is a MORE soft-key (upper-left and/or upper-right soft-key for the other parameters.
boB
Thanks, forgot that step from 5 years ago!